How to config ComX200 to make it is working as a gateway?

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • How to config ComX200 to make it is working as a gateway?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
ryan_wang
ryan_wang Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-08-25 04:24 PM

2 Likes
8
2425
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-25 04:24 PM

How to config ComX200 to make it is working as a gateway?

Hi Guys,

I am setting up a testing system to use ComX200 with firmware v1.1.20 as a gateway, the system structure please see below. In the system, ComX200 can communicate with downstream device PM5350 and ION6200 via EGX300 properly. But PME cannot talk to PM5350 (set up ComX as a gateway site in PME), and I don’t know how to configure PME to talk to ION6200. Does firmware 1.1.20 support gateway functionality?

Any comments and suggestions are welcome.

4400




 
 
 
 
 
 
 
 
 
 
 
 





Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2014-08-26 08:42 AM

3 Likes
5
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-26 08:42 AM

The Modbus gateway features is only available for interfaces that are not dedicated to the wan.

If the Com'X 200 is configured with 2 separated IP networks,

  • the modbus gateway features will only work for interface eth2
  • the modbus gateway features will not work for interface eth1

If the Com'X 200 is configured with 2 switched IP networks,

  • the modbus gateway features will work for interface eth1 and eth2

This rules has been implemented  in order to enforce ensure cybersecurity :

If the customer wants to separated the network between

  • "Publication network" (public, connected to the wan) and
  • "Acquisition network" (private and reserved technical devices),

It seems logical to disable anybody from the pubic network to send modbus request to any devices connected to the com'X 200

Please consult pages 35-36 of the design guide for more details

Regards

See Answer In Context

Reply
Replies 8
dborle
dborle Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-08-25 10:33 PM

0 Likes
1
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-25 10:33 PM

Hi Ryan,

I found the same problem with the Com'X here in our office (also if it is version 1.1.14). It is impossible to access the Com'X as a gateway neither with PME nor with Modscan or PMCModbus. The connection is always timing out. I have also reported this problem to the technical support.

Daniel

Reply
Anonymous user
Not applicable

Posted: ‎2014-08-26 08:42 AM

3 Likes
5
2270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-26 08:42 AM

The Modbus gateway features is only available for interfaces that are not dedicated to the wan.

If the Com'X 200 is configured with 2 separated IP networks,

  • the modbus gateway features will only work for interface eth2
  • the modbus gateway features will not work for interface eth1

If the Com'X 200 is configured with 2 switched IP networks,

  • the modbus gateway features will work for interface eth1 and eth2

This rules has been implemented  in order to enforce ensure cybersecurity :

If the customer wants to separated the network between

  • "Publication network" (public, connected to the wan) and
  • "Acquisition network" (private and reserved technical devices),

It seems logical to disable anybody from the pubic network to send modbus request to any devices connected to the com'X 200

Please consult pages 35-36 of the design guide for more details

Regards

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2014-08-26 10:12 AM

1 Like
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-26 10:12 AM

Here are the excerpts from the Design Guide:

4406

4407

James

Reply
ryan_wang
ryan_wang Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-08-26 03:50 PM

1 Like
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-26 03:50 PM

Hi Daniel, I got you case in our support system. I will get you back after I verify the both structure, 2 seperated IP and 2 switched IP.

Technically, ComX200 supports two kinds of gateway configuration which can be found at page 35 and 36 in design guide that can be downloaded at . You can see the tests I am doing below, maybe you would like to do some tests on your device according to design guide to see if they works fine.

Reply
ryan_wang
ryan_wang Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-08-26 05:01 PM

1 Like
3
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-26 05:01 PM

Hi Jef & James,

Thank you very much for your answers which is very helpful to make me understand the strategy of ComX200 working as a gateway. Today, after going throught the gateway part of design guide, I changed my network and did further tests, but PME still cannot talk to the downstream device under ComX200. Could you do me a favor to help to check my system configuration to see if there are wrong settings on them? Does the firmware v1.1.20 support gateway funcation?

1. Sperated IP address

ComX200 connects to PM5350 properly, The configuration page of ComX200 can be login to from the machine hosting PME via IP 10.25.1.1.

PME can reach to ION6200 which is connected to EGX300, but cannot talk to PM5350 successfully.

4410

2. 1 IP for both ports

On the computer hosting PME can access into ComX200 configuration page via IE, but PME cannot connect to PM5350 successfully.

4411

Thanks,

Ryan

Reply
ryan_wang
ryan_wang Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-08-27 11:26 AM

1 Like
2
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-27 11:26 AM

Today, both of the strucure are working properly, for the seperated IP system I fouud that the default gateway setting of network connection on the machine hosting PME was 10.24.1.1, I changed it to 10.25.1.1, then PME can talk to downsterad devics successfully.

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2014-08-27 11:54 AM

0 Likes
1
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-27 11:54 AM

Thanks..this was confusing me as to why you were having this issue.

Did you make any changes?

James

Reply
ryan_wang
ryan_wang Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-08-27 11:59 AM

2 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-27 11:59 AM

The only change I made is to correct the Default gateway setting for Local Area Connection from 10.24.1.1 to 10.25.1.1.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore