Gateway (EGX, PAS...) to PME and EBO simultaneously

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Gateway (EGX, PAS...) to PME and EBO simultaneously
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Christian_Sáenz
Lieutenant JG Christian_Sáenz Lieutenant JG
Lieutenant JG

Posted: ‎2023-01-05 12:22 PM

0 Likes
3
3076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-05 12:22 PM

Gateway (EGX, PAS...) to PME and EBO simultaneously

Hi team;

 

We have a site with EBO and PME integrated to the main headquarters. The client is a bank. They want to monitor other branches where there are currently no EBOs or PMEs. For this monitoring, the easiest thing is to place an Automation Server (brain of our BMS: EBO, which has native Bacnet, Modbus and LonWorks) but for the price it is not viable because this branch will be the "demo" for another 90 that have.
The question is: according to the attached diagram, T1, T2 and T3 are TH900 family thermostats (https://www.se.com/us/en/download/document/F28152/) to sense temperatures and they will be placed in a SD duct sensor; Also, M1 is a basic range meter, eg iem3000, PM2120 or similar. This will be integrated into a gateway (EGX initially or its PAS equivalent) and the intention is to bring the gateway to EBO and PME simultaneously, but the question is, can the gateway report simultaneously to EBO and PME? If not, can these variables be entered into the PME through the gateway and via webservices, ETL or similar, transfer them to the EBO or vice versa? Or what would be the option?
Also, if you have any suggestions for another type of thermostat, architecture, topology, it is welcome.

 

Please, thanks!

 

 

Attachments
Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-01-06 01:29 AM . Last Modified: ‎2023-01-06 01:30 AM

0 Likes
0
3046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-06 01:29 AM

Hello @Christian_Sáenz , 

 

As you mentioned, it is always better to install one (or more) AS-P on your building (depending on the size). then déclare the Modbus Table on EBO. This will allow you to control your meter and T900 sensors from EBO Webstation (or Workstation).

 

At gateway level I do not see any restriction, because a Panel Server can be a transparent gateway for your T900 sensors. Modbus registers will be forwarded to upstream system. Then you can connect the Panel Server on both PME and EBO.

 

Now let's discuss EBO and PME.

You need to know that integration between PME2022 and EBO 4.0.2 is now easier because PME2022 integrate an EWS Client (EcoStruxure Web Services).

PME_EBO_EWS.jpg

=> By doing this, you can connect your gateway only on PME or EBO. Do the job only 1 time.

 

Some references here:

  • https://digital-energy-help.se.com/pme/content/11_other_content/energyexpert/overview/overview.htm
  • https://digital-energy-help.se.com/pme/content/11_other_content/energyexpert/design/architectures.ht...

If you are using previous version of PME and EBO, this is also possible:

  1. if you connect the gateway + devices on PME => you will need to use the PME EWS Server to transfer data from PME to EBO
  2. if you connect the gateway + devices on EBO => you will need the ETL tool to transfer data from EBO (Extended Trending Logs) and PME.

Let us know if you have more questions.

 

Regards,  

 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 3
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2023-01-05 12:28 PM

1 Like
0
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-05 12:28 PM

The gateway doesn't report data to EBO or PME.  PME and/or EBO will request data via the Gateway.  So, to answer your question, yes, the Gateway can handle requests from more than one client.

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-01-05 11:03 PM

1 Like
0
3057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-05 11:03 PM

Just to complement, EBO, PME, "EGX"= modbus tcp gateway,  need to be connected to a network able to route modbus tcp traffic (tcp port 502)...

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-01-06 01:29 AM . Last Modified: ‎2023-01-06 01:30 AM

0 Likes
0
3047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-06 01:29 AM

Hello @Christian_Sáenz , 

 

As you mentioned, it is always better to install one (or more) AS-P on your building (depending on the size). then déclare the Modbus Table on EBO. This will allow you to control your meter and T900 sensors from EBO Webstation (or Workstation).

 

At gateway level I do not see any restriction, because a Panel Server can be a transparent gateway for your T900 sensors. Modbus registers will be forwarded to upstream system. Then you can connect the Panel Server on both PME and EBO.

 

Now let's discuss EBO and PME.

You need to know that integration between PME2022 and EBO 4.0.2 is now easier because PME2022 integrate an EWS Client (EcoStruxure Web Services).

PME_EBO_EWS.jpg

=> By doing this, you can connect your gateway only on PME or EBO. Do the job only 1 time.

 

Some references here:

  • https://digital-energy-help.se.com/pme/content/11_other_content/energyexpert/overview/overview.htm
  • https://digital-energy-help.se.com/pme/content/11_other_content/energyexpert/design/architectures.ht...

If you are using previous version of PME and EBO, this is also possible:

  1. if you connect the gateway + devices on PME => you will need to use the PME EWS Server to transfer data from PME to EBO
  2. if you connect the gateway + devices on EBO => you will need the ETL tool to transfer data from EBO (Extended Trending Logs) and PME.

Let us know if you have more questions.

 

Regards,  

 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore