Hello,
A customer want's to upgrade his Com'X current version 1.0.14 to the version 3.0.7. But without succes.
I have noticed in version 3.5 they tell to first upgrade to version 2.1 before to upgrade to 3.5, does this apply also to version 3.0.7
And is there a place wher we can download the old firmware versions, on shoppingKiosk i can only find 3.0.7 and 3.5
Kind Regards
Koen
Link copied. Please paste this link to share this article on your social media post.
Hello Koen,
Version 2.1 of the firmware should be installed prior to installation of version 3.5 as well. Here is a link to version 2.1:
Link copied. Please paste this link to share this article on your social media post.
Hello Koen,
Version 2.1 of the firmware should be installed prior to installation of version 3.5 as well. Here is a link to version 2.1:
Link copied. Please paste this link to share this article on your social media post.
Hi Steven,
Will that firmware work on a Com'X 510 (It says Com'X 200)?
Regards,
Theren
Link copied. Please paste this link to share this article on your social media post.
Hello Theren, I apologize, I meant to sent this link:
ComX510_v2.1.17.zip - Box
I have fixed the link above as well.
Link copied. Please paste this link to share this article on your social media post.
Thank you Steven.