Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Easergy P3 integration to Com'X 510

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Easergy P3 integration to Com'X 510
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Digital_Hastak
Lieutenant JG Digital_Hastak Lieutenant JG
Lieutenant JG

Posted: ‎2020-09-07 09:09 AM . Last Modified: ‎2020-09-07 09:10 AM

0 Likes
2
1434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-07 09:09 AM

Easergy P3 integration to Com'X 510

Hi community, 

 

I understand usual integration of Easergy relays is into PME, and hence PME has native driver for it.

 

However, I am looking at an application for Easergy P3 in SM6 relay to be connected upto Facility Expert Operations cloud service for remote monitoring and alarm in CIB segment. 

 

Has anyone worked on or created Easergy custom device within Com'X, that you can share? 

 

 

sm6 + fe.png

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2020-09-17 03:58 AM . Last Modified: ‎2025-11-24 04:15 AM

2 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-17 03:58 AM

Hello @Digital_Hastak , 

As you mentionned PME /PSO have a native driver for P3 relay : 

https://community.se.com/t5/EcoStruxure-Power-Monitoring/PME-2020-9-0-CU2-SE-Driver-for-Easergy-P3/m...

https://community.se.com/t5/EcoStruxure-Power-Monitoring/Easergy-P3-Driver-for-PME-9-0/m-p/169200?se...

https://community.se.com/t5/EcoStruxure-Power-Monitoring/PME-2020-9-0-CU2-SE-Driver-for-Easergy-P3/m...

 

From a business point of view : P3 is not in the segment of Facility Expert that is more dedicated to small and medium buildings.

 

I never heard that a P3 custom model was developed for Com'X510.

 

Be careful because :

  • P3 relay have a dynamic modbus map :
  • it means you need to develop your own custom model depending on your specific P3 configuration : https://www.se.com/ww/en/faqs/FA404418/
  • you will need to create custom event on the Com'X to raise custom alarms on FE

 

 

Regards.

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Anonymous user
Not applicable

Posted: ‎2020-09-17 03:40 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-17 03:40 AM

Hi the community members can you help this member on this topic, please?

 

@Romain_Polette do you think you can advise on this topic?

 

Have a nice day.

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2020-09-17 03:58 AM . Last Modified: ‎2025-11-24 04:15 AM

2 Likes
0
1425
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-17 03:58 AM

Hello @Digital_Hastak , 

As you mentionned PME /PSO have a native driver for P3 relay : 

https://community.se.com/t5/EcoStruxure-Power-Monitoring/PME-2020-9-0-CU2-SE-Driver-for-Easergy-P3/m...

https://community.se.com/t5/EcoStruxure-Power-Monitoring/Easergy-P3-Driver-for-PME-9-0/m-p/169200?se...

https://community.se.com/t5/EcoStruxure-Power-Monitoring/PME-2020-9-0-CU2-SE-Driver-for-Easergy-P3/m...

 

From a business point of view : P3 is not in the segment of Facility Expert that is more dedicated to small and medium buildings.

 

I never heard that a P3 custom model was developed for Com'X510.

 

Be careful because :

  • P3 relay have a dynamic modbus map :
  • it means you need to develop your own custom model depending on your specific P3 configuration : https://www.se.com/ww/en/faqs/FA404418/
  • you will need to create custom event on the Com'X to raise custom alarms on FE

 

 

Regards.

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore