Dear all,
One of my customer is trying to get rid of pulse counting and would like to use signal converters instead.
They are asking us about the possible integration of that kind of device with their existing install base (EGX300 + PM meters).
I attached the converter specifications sheet to that post to understand that device capabilities.
Does anyone have experience with interfacing a signal converter from Krohne?
Does it even sound feasible to you?
Thanks in anticipation!
-Maxence
Link copied. Please paste this link to share this article on your social media post.
Salut Maxou,
Your documentation states that it seems to have an optional modbus port. If that's the case, then it's a piece of cake. You can simply use a custom device type with the EGX300 or the Com'X200 and you'll be done.
You can find the modbus register reads here!
Let me know if I can help further.
Link copied. Please paste this link to share this article on your social media post.
Salut Maxou,
Your documentation states that it seems to have an optional modbus port. If that's the case, then it's a piece of cake. You can simply use a custom device type with the EGX300 or the Com'X200 and you'll be done.
You can find the modbus register reads here!
Let me know if I can help further.