Com'X200 Custom Device Type

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X200 Custom Device Type
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
LaurentCoene
Captain LaurentCoene Captain
Captain

Posted: ‎2013-08-16 01:22 AM

2 Likes
0
786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-08-16 01:22 AM

Com'X200 Custom Device Type

Just like for the EGX300, the Com'X can talk to anything that talks Modbus.

So let's see how this is done! For our test, we connected the following:

  • PM5350 - we wanted to add the Pulse out
  • CWLP Modbus Temperature/Humidity/CO2 sensor from Veris

Interestingly the Com'X200 will allow you to create multiple devices using the same modbus id. A really welcome feature that was not allowed in the EGX300 as now you can have the "standard" information and you can create a second device for the additional stuff. Once in Energy Operation, you can obviously group everything together.

PM5350 Custom Device Type

First I added the standard PM5350. Couldn't be easier:

  • Go to the Device Settings tab
  • Select the Com'X200 device in the tree on the left
  • Click on Discover Connected Devices at the bottom of the tree
  • Click Start in the new windows

Done!

2075

Next, let's create our new Custom Device:

  • Again, select the Com'X200 in the tree
  • On the right pane, go to the Modbus Serial section
  • In the last drop down, select "Create a new device"

2076

  • In the new screen, in the Device Type drop-down, go to the end of the list and select "Modbus RTU generic slave".

2077

  • In the Configuration Pane, enter the Modbus ID (Slave Id)
  • Select the Usage
  • Click on Create
  • A new Modbus RTU slave will appear in the tree under Modbus Serial; Select it.
  • On the right pane, the configuration settings for your new device type will appear. In the Slave section, click on New Frame
  • There, the configuration is very similar to the EGX300 except that the numbers start from 0 (not 1), which means that when you read a register list together, remember to put your starting address as register address - 1. As defined in the PM5350 register list, enter the DO1 pulse count register address - 1: 9674
  • Click on Edit Frame
  • Click on New item
  • Enter the Custom name, Format, and Custom Unit

2078

Click Ok, Save Changes and you will start seeing the current value in the Measurement Table section right after the Slave section on your right pane.

CWLP Through Modbus TCP Custom Device Type

For our CWLP, we wanted to add some extra spice, so we connected it to a networked EGX300 (note that it could have been done with an EGX100 too).

  • Select the Com'X200 in the tree
  • Then in the right pane, look for the Ethernet section. In the drop down, select Create a new device.
  • Select the device type and click on Create
  • Thew new EGX300 will appear in your tree. Select it
  • Enter the IP of your EGX in the Configuration --> Host section
  • Click Save Changes
  • Go to the Modbus Serial section of your EGX300 and again select Create a new device
  • Select Modbus RTU Generic Slave

2079

  • In the tree, select your new Modbus RTU Generic Slave object
  • Just like the PM5350, you can create your new frames and enter the registers (remember - 1)

2080

Last comment, you will notice while entering the items that you can convert the communicated values to what it really is. You can also use that to work out the decimals displayed.

Tags (4)
  • Tags:
  • com'x200
  • custom
  • device
  • type
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore