EGX300 Firmware v4.300.zip

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • EGX300 Firmware v4.300.zip
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2013-03-05 02:01 PM

4 Likes
4
1549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-03-05 02:01 PM

EGX300 Firmware v4.300.zip

Just released!!!

Downloads

EGX300 Firmware   & Disk Image Update

Version   4.300 firmware provides:

·            Improved   Custom Device Type Generator support – added offset

·            Resolution   to Daylight Savings Time not operating correctly in the Southern Hemisphere

·            HTTP   Proxy Support for Data Export

·            Resolution   to issue exporting via SSL to IIS Web Server

·            Disk   Image Version is displayed in the Web Interface

Version   4.300 Disk Update provides:

·            Ability   to save Dashboard images

·            Russian   and Japanese Language support

·            Support   for the following devices.

o      EM7320

o      EM7380

o      PM5350BW

*Upgrading   to version 4.300 requires new firmware to be downloaded to the EGX followed   by the egx04300.upd Disk Image. 

Firmware Download Instructions for EGX300

Currently Running Firmware Version 3.7xx

Updating   to version 4.300 from version 3.7xx requires all data log files to be   converted internally.  This conversion   will be executed at the first boot after the download.  While converting the data log files, browsing   of the EGX will be limited to a page displaying the status of the conversion   until conversion is complete.    Depending on the size and number of the data log files this process   may take several minutes. 

Before   downloading the firmware logging must be disabled.  It is recommended the user save all data log   files to external storage before downloading.    Refer to the EGX300 User’s Guide for instructions on how to disable   logging and remove data log files. 

1.       Disable   Logging.

2.       Save   data log files to external storage (optional but recommended).

3.       Remove   data log files (optional but recommended).

4.       Transfer   the version 4.300 firmware file (egx04300.bin) to your computer.

5.       Use   FTP to copy the “egx04300.bin” file from your computer to the EGX300.  The status LED will flash rapidly while the   firmware is being programmed.  Do not remove power during this time.  Once the download is complete the EGX will   automatically reboot.  Refer to the   EGX300 User’s Guide if you need more information.

6.       Allow   the EGX to reboot after the firmware file transfer, then browse the EGX300   Diagnostic Statistics page and confirm V4.300 is displayed as the Firmware   Version in the Gateway Information section.   

7.       After   confirming the firmware has been updated apply the V4.300 Disk Update.


Firmware Download Instructions for EGX300

Currently Running Firmware Version 3.800 or Greater

Before   downloading the v4.300 firmware it is recommended to disable logging and to save   all data log files to external storage.    Refer to the EGX300 User’s Guide for instructions on how to disable   logging and remove data log files. 

1.       Disable   Logging.

2.       Save   data log files to external storage (optional but recommended).

3.       Remove   data log files (optional but recommended).

4.       Transfer   the version 4.300 firmware file (egx04300.bin) to your computer.

5.       Use   FTP to copy the “egx04300.bin” file from your computer to the EGX.  The status LED will flash rapidly while the   firmware is being programmed.  Do not remove power during this time.  Once the download is complete the EGX will   automatically reboot.  Refer to the   EGX300 User’s Guide if you need more information.

6.       Allow   the EGX to reboot after the firmware file transfer then browse the EGX300   Diagnostic Statistics page and confirm 4.300 is displayed as the Firmware   Version in the Gateway Information section.   

7.       After   confirming the firmware has been updated apply the V4.300 Disk Update.

Attachments
v4.300.zip
Tags (10)
  • Tags:
  • 4.300
  • custom_device_type_generator
  • dashboards
  • egx300
  • em7320
  • em7380
  • firmware
  • japanese
  • pm5350
  • russian
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Digital_Hastak
Lieutenant JG Digital_Hastak Lieutenant JG
Lieutenant JG

Posted: ‎2013-03-05 03:13 PM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-03-05 03:13 PM

Hi James, I tried updating two of my EGX300 currently. With both of them Firmware upgrade (.bin) file worked well, however, while putting a update patch (.upd) file, it gave me below error "An error occurred copying a file to the FTP Server. Make sure you have permissionto put files on the server. Details: The Connection with the server was reset."

With the first one after several attempts, it was resolved and was able to update the patch. Not with the second one.

  Video Link : 1024

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2013-03-05 07:24 PM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-03-05 07:24 PM

Hello Hastak.

How long did you wait before trying to apply the v4.300.upd disk update?  Perhaps this is the issue??  Once you copy the EGX300 firmware to the box via FTP...it needs to reboot the box.  You must wait for it to come back online before applying the patch in the same maner...once again, a reboot  I updated the EGX300 Demo Site this afternoon, and did not have any issues, but let me know what you find.

What do you see on the bottom left hand side of your EGX300?  Which Disk Image Version shows?

1079

Thanks,

James

Reply
Digital_Hastak
Lieutenant JG Digital_Hastak Lieutenant JG
Lieutenant JG

Posted: ‎2013-03-05 07:28 PM

1 Like
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-03-05 07:28 PM


Hi James, Yes I did wait till it reboots. However since then I have been able to figure out the way and I have update 2 more EGXs since then.

What I did initially was copy both bin file and upd file in System folder, one after the other. But what I did now was copied the bin file in System folder and dropped the upd file in main ftp folder on EGX. And it works perfect!

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2013-03-05 07:33 PM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-03-05 07:33 PM

Perfect...let me know if you have any additional feedback about the 4.3 release. Thanks!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore