Hi,
Is anyone know why I lost the connection with two PM800 meter connected in the same EGX100 and after a few hours it return ?
Best regards.
Link copied. Please paste this link to share this article on your social media post.
Please check if PoE is powered on, while the power supply for the EGX is connected in parallel. If so, just disconnect the power supply of the EGX.
Link copied. Please paste this link to share this article on your social media post.
Except check PoE power supply, please check:
1) Was terminal resistance (120 ohm) connected correctly?
2) RS-485 shield ground should be one side connection instead of loop ground. It should be connected on one side, not connected on both sides.
Link copied. Please paste this link to share this article on your social media post.
Hi Amine,
Please check the answers from Alexander and Jun and assess if those are describing your PM800 connections situation or if they help.
Regards,
Adrian
Posted: 2015-04-07 08:58 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Adrian,
I haven't check those answers in site but if i solve this probleme i will contact you.
Best regards.
Posted: 2015-04-07 08:58 AM
Link copied. Please paste this link to share this article on your social media post.
Thank you very uch for your help.
Link copied. Please paste this link to share this article on your social media post.
You are welcome to contact us if you require further assistance.