The easiest method for me, was this, assuming that the Link150 in your office network which has DHCP Service:
- to press the Reset pin (not !! the round white R button) for 1 to 5 seconds.
When the IP reset pin is pressed for 1 to 5 seconds, the IP acquisition mode is reset to the factory default (DHCP).
- the go to your Windows PC and open My Computer > Network > Other Devices; there should be your Link150 device appearing!
- double click that icon and the default web browser will open the Link150 web page (so you don't have to search for the dynamic IP address)
If not in the above situation, in the QuickStart Guide, page 7.
Here is where to find all the required docs:
Posted: 2017-01-08 06:01 PM
Link copied. Please paste this link to share this article on your social media post.
Help me
Link copied. Please paste this link to share this article on your social media post.
The easiest method for me, was this, assuming that the Link150 in your office network which has DHCP Service:
- to press the Reset pin (not !! the round white R button) for 1 to 5 seconds.
When the IP reset pin is pressed for 1 to 5 seconds, the IP acquisition mode is reset to the factory default (DHCP).
- the go to your Windows PC and open My Computer > Network > Other Devices; there should be your Link150 device appearing!
- double click that icon and the default web browser will open the Link150 web page (so you don't have to search for the dynamic IP address)
If not in the above situation, in the QuickStart Guide, page 7.
Here is where to find all the required docs:
Link copied. Please paste this link to share this article on your social media post.
Ta Cong:
I endorse what Adrian has said. That is something fix in the Link 150 over the older EGX models. Past models required us to use a serial port and hyper-terminal with crossover or special cables. DB9 ports and hyper-terminal are nearly extinct. WireShark can be your friend. It may be considered a bit messy and you need to know where to look but can also help you break into some devices when the IP is unknown.
Sincerely,
Michael
Link copied. Please paste this link to share this article on your social media post.
Try 169.254.yy.zz with yy and zz being the last two decimal numbers of the MAC address. So the pdf from Schneider claims.....
Link copied. Please paste this link to share this article on your social media post.
Posted: 2017-01-10 08:47 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Adrian,
Thanks very much for information of you. This is all what is search.
But Adrian, so i cannot change IP address of Link 150 like that EGX100
Posted: 2017-01-10 08:48 AM
Link copied. Please paste this link to share this article on your social media post.
HI Michael Franz,
So, I cannot change IP address of Link 150 like that EGX100.
Thanks you.
Link copied. Please paste this link to share this article on your social media post.
You can change the IP. It is similar to doing so on an EGX 100. It has the additional ability to be discovered on a network with Windows Explorer.
See the capture here...
WireShark should also be able to return a default IP at boot-up of the gateway.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2017-01-12 08:15 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Michael Franz,
Thanks for your information
It really useful.
Link copied. Please paste this link to share this article on your social media post.
You are welcome - any time. I have worked with many gateways including the original MMS version. Even have one for the memories.