Documentation on 'Wireless Device Type Codes'

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Documentation on 'Wireless Device Type Codes'
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
96
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
Breina
Ensign Breina
Ensign

Posted: ‎2024-04-17 10:41 AM

0 Likes
10
1015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-17 10:41 AM

Documentation on 'Wireless Device Type Codes'

The PowerTag Link documentation (DOCA0157EN-07.pdf) had a table mapping Device Code and Identifiers to Device Types;

Breina_0-1713375217532.png

The Panel Server documentation (DOCA0172EN-09.pdf and DOCA0241EN-06.xlsx) don't have such a table. Was wondering if there's one that's maintained more recently. I have a user with a product identifier of '17973', and I'm not sure what the device's capabilities are.

 

I'm sure I've missed it somewhere, please help me find it?

Thanks in advance! 🙂



Dev of the Panel Server HomeAssistant integration
  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-04-30 05:25 AM

0 Likes
1
929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-30 05:25 AM

Hello @Breina , 

 

Why not using the Modbus function code 43-14 to read device identification ?

Table in your post is related to Modbus Registers 31025 and 31032 for any wireless device connected to the old PowerTag Link. 31025 not applicable to the Panel Server.

 

For Panel Server only register 31032 "Wireless product identifier" is available, but.... I cannot find any public documentation explaining returned values...

 

FYI 17973 = PowerTag Rope Sensor R200 for IEC Market. Codes in the PowerTag Link table are not all listed.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2024-05-07 05:05 AM

1 Like
0
852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-07 05:05 AM

@Romain_Polette 

For modbus deviced, PaS is not maintaining any modbus data for a downstream modbus serial device.
In case of modbus serial devices, PaS will be transparent for all the queries from upstream SCADA and it will be routed to the end device and the response we are getting is from end device only. That s why you have noticed that  Function Code 43-14 requests are answered correctly.

For Zigbee devices it is not the same mecanism, as this time the PaS that maintains and manage data and PaS does not answer to modbus device identification requests with function code 43-14

See Answer In Context

Reply
Replies 10
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-04-30 05:25 AM

0 Likes
1
930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-30 05:25 AM

Hello @Breina , 

 

Why not using the Modbus function code 43-14 to read device identification ?

Table in your post is related to Modbus Registers 31025 and 31032 for any wireless device connected to the old PowerTag Link. 31025 not applicable to the Panel Server.

 

For Panel Server only register 31032 "Wireless product identifier" is available, but.... I cannot find any public documentation explaining returned values...

 

FYI 17973 = PowerTag Rope Sensor R200 for IEC Market. Codes in the PowerTag Link table are not all listed.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Breina
Ensign Breina
Ensign

Posted: ‎2024-05-01 03:54 AM

0 Likes
0
917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-01 03:54 AM


@Romain_Polette wrote:

Hello @Breina , 

 

Why not using the Modbus function code 43-14 to read device identification ?

Table in your post is related to Modbus Registers 31025 and 31032 for any wireless device connected to the old PowerTag Link. 31025 not applicable to the Panel Server.

 

For Panel Server only register 31032 "Wireless product identifier" is available, but.... I cannot find any public documentation explaining returned values...

 

FYI 17973 = PowerTag Rope Sensor R200 for IEC Market. Codes in the PowerTag Link table are not all listed.

 

Regards, 


Hi Romain,

 

Thanks for the suggestion! I can retrieve the Panel Server's identification this way (slave 0xFF), but when prompting wireless devices for this (slaves 100 and up) they respond with 'Illegal function'.

 

I'm fine with just retrieving commercial references for Panel Servers and PowerTag Links, but SmartLinks do not support this function; it seems to rely exclusively on the wireless device codes (DOCA0115EN-03.pdf).

Breina_0-1714559732037.png

I would love to keep my software compatible with all old devices, yet up-to-date with all future EcoStruxture developments. Is there any chance you could publicise an updated table for this?

 

Regards,

Brecht



Dev of the Panel Server HomeAssistant integration
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-05-01 11:37 PM

0 Likes
1
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-01 11:37 PM

Hello @Breina , 

 

You are right... PowerTag is not supporting Function code 43-14 through Panel Server...

But it works well through PowerTag Link (see below):

Romain_Polette_0-1714578550731.png

 

This is strange because Modbus Serial devices connected to Panel Server support the Function Code 43-14:

Romain_Polette_1-1714578708724.png

 

@Eric_HAVAS can you check if this is expected with 1.9 ?

  • Function Code 43 not supported for Wireless devices -> Exception 1 (Illegal Function) returned
  • Function Code 43 OK for wireless devices on PowerTag Link

Thanks !

Romain POLETTE
Solution Architect - France Operations
Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2024-05-07 05:05 AM

1 Like
0
853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-07 05:05 AM

@Romain_Polette 

For modbus deviced, PaS is not maintaining any modbus data for a downstream modbus serial device.
In case of modbus serial devices, PaS will be transparent for all the queries from upstream SCADA and it will be routed to the end device and the response we are getting is from end device only. That s why you have noticed that  Function Code 43-14 requests are answered correctly.

For Zigbee devices it is not the same mecanism, as this time the PaS that maintains and manage data and PaS does not answer to modbus device identification requests with function code 43-14

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-05-12 09:45 PM

1 Like
1
819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-12 09:45 PM

hello @Eric_HAVAS ,

Why do we have a difference between PAS and PTL as highlihgted by @Romain_Polette  ?

Thanking in advance

Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2024-05-13 05:38 AM . Last Modified: ‎2024-05-14 11:52 PM

0 Likes
0
803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-13 05:38 AM

Hello @Guillaume_Evrard 
It's only a question of priority and (over)load of backlog.
Due to the list of features still to develop to give more and more value added to the Panel Server gateway,  the function 03 has been considered more priority to develop than the others function codes. (FC 43-14)

Eric_HAVAS_0-1715603496602.png

(Screenshot of this excel file extracted from the list of modbus functions supported by the Panel  Server  https://www.se.com/ww/en/download/document/DOCA0241EN/  )

 

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-05-13 06:21 AM

0 Likes
0
789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-13 06:21 AM

thanks a lot @Eric_HAVAS for your answer.

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-05-13 09:23 AM

0 Likes
0
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-13 09:23 AM

Hello !

 

According to the documentation, this seems possible with PowerTag sensors connected to child Panel Server, because child PTag will be considered as Modbus TCP devices.
Am I right ?

 

Romain POLETTE
Solution Architect - France Operations
Reply
Breina
Ensign Breina
Ensign

Posted: ‎2024-05-14 03:12 AM

1 Like
0
763
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-14 03:12 AM

Alright thanks for the info all! For now, I'll use commercial reference to identify devices and I'll be looking forward to using FC 43-14 some time in the future. 🙂



Dev of the Panel Server HomeAssistant integration
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-05-15 01:42 AM

1 Like
0
749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-15 01:42 AM

Hello @Breina , 

FYI, I've sent a request to update Panel Server Modbus documentation to integrate more info about "Wireless Product Identifier" (to align with PowerTag Link documentation).

 

I have no release planning at this time. Stay tuned.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of