Posted: 2015-07-21 04:13 AM
Link copied. Please paste this link to share this article on your social media post.
Hi All,
I have an issue when I try to connect ION7650 to PME 7.2 using EGX 100 and COM2: there is no data displayed in the EGX100 registers or in PME7.2.
The ION7650 configuration is :
The EGX configuration is:
When i try to read registers in EGX100 i have no values :
The ION7650 is connected with several PM870 to the EGX100 via RS485 liaison.
I can't find where is the problem?
Need your help on this.
Best regards.
Link copied. Please paste this link to share this article on your social media post.
Hi Amine,
I have checked and found that you should fill the Input address on EGX100 start from 150, not 40150 as you did
By this way, I can read data from ION, no need to configure anything more
Please try again!
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Hi Amine,
I see your GTW can read data from ION7650 without error. So, the problem if any just in Mapping for Modbus Communication in ION7650
I think you're using the Defult Mapping for ION7650, but someone ( may be factory ) has changed Mapping by update Template for this Meter
First, access to check the Mapping inside of ION7650 by IONsetup
a. Connect ION 7650 to IONsetup via Ethernet port
b. Check in Communication/3rd Party Protocols, choose Modbus Slave tab
c. Choose default profile in Map name column, and click Edit
d. At this step, you can check/re-config your mapping for each parameter....
e. Print-out this Mapping for using later
f. Re-check the Data of EGX as you did above steps
Hope it helps you
Best Regards
Posted: 2015-07-21 04:53 AM
Link copied. Please paste this link to share this article on your social media post.
Hi,
Thank you very much for feedback.
I checked the mapping in the default map, when i try to read for exemple Ia in EGX100 ( 40150 Adress) it still display no value :
=
I didn't modify any things in IONsetup :
is there any specific configuration to do in IONsetup ?
Best regards.
Link copied. Please paste this link to share this article on your social media post.
Hi Amine,
I will test again with real ION Meter and revert to you soon
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Posted: 2015-07-23 06:22 AM
Link copied. Please paste this link to share this article on your social media post.
Hi,
Thank you very much for help.
That works.
Best regards.