Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
28 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hello everyone.
I have a customer that he has a EGX100 and in the MODBUS there are about 20 power meters. He has PM710, PM5560 and ION6200.
He has the EGX100 connected to a EGX300, and he can see all power meters registers, except the ION6200.
The MODBUS was checked and its OK. Electrical conections are fine.
Wich can be the problem, any have any idea?
Thanks for all.
Link copied. Please paste this link to share this article on your social media post.
Hello,
I am not 100% what you mean by "The MODBUS was checked and its OK." if this checking the wires or the modbus settings on the ION 6200 meter. The ION 6200 Meter has a setup register that determines what protocol the meter talks. either PML or Modbus. Will want to check that the meter is set to talk modbus.
Link copied. Please paste this link to share this article on your social media post.
Thanks, I will check it!
Link copied. Please paste this link to share this article on your social media post.
Hi Carlos,
What did you find?
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.