Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
User | Count |
---|---|
111 | |
53 | |
46 | |
32 |
Link copied. Please paste this link to share this article on your social media post.
Hello everyone.
I have a customer that he has a EGX100 and in the MODBUS there are about 20 power meters. He has PM710, PM5560 and ION6200.
He has the EGX100 connected to a EGX300, and he can see all power meters registers, except the ION6200.
The MODBUS was checked and its OK. Electrical conections are fine.
Wich can be the problem, any have any idea?
Thanks for all.
Link copied. Please paste this link to share this article on your social media post.
Hello,
I am not 100% what you mean by "The MODBUS was checked and its OK." if this checking the wires or the modbus settings on the ION 6200 meter. The ION 6200 Meter has a setup register that determines what protocol the meter talks. either PML or Modbus. Will want to check that the meter is set to talk modbus.
Link copied. Please paste this link to share this article on your social media post.
Thanks, I will check it!
Link copied. Please paste this link to share this article on your social media post.
Hi Carlos,