Hi,
We have a case where customer has 40 meters to be viewed from a single webpage. He doesn't want a dedicated PME and wants to view only basic parameters (V,I,Kwh).
We want to propose ComX510 with following configuration:
24 devices connected directly to ComX510
EGX100/300 - For balance 16 devices. This EGX will then be connected to ComX510.
What I'd like to know is in such case, can we view data for all the downstream devices connected through EGX100/300 on ComX510 webpage?
Also, is it possible to store data from those devices on to memory of COmX510? If yes, can we use that data to generate dashboards in ComX510 for devices connected through EGX.
Also, is it possible to take a csv dump for all 40 devices from ComX510 at a regular interval?
James Jeanette If you can give some inputs on above points.
Link copied. Please paste this link to share this article on your social media post.
Hello Gaurang.
What I'd like to know is in such case, can we view data for all the downstream devices connected through EGX100/300 on ComX510 webpage?
Yes...the Com'X 510 is designed for this case. My only caution would be that the number of connected devices can be dependent on which devices, and how often logged.
Also, is it possible to store data from those devices on to memory of COmX510? If yes, can we use that data to generate dashboards in ComX510 for devices connected through EGX.
Yes...no problem
Also, is it possible to take a csv dump for all 40 devices from ComX510 at a regular interval (say every hour)?
Yes...no problem
I hope this helps,
James
Link copied. Please paste this link to share this article on your social media post.
Hello Gaurang.
What I'd like to know is in such case, can we view data for all the downstream devices connected through EGX100/300 on ComX510 webpage?
Yes...the Com'X 510 is designed for this case. My only caution would be that the number of connected devices can be dependent on which devices, and how often logged.
Also, is it possible to store data from those devices on to memory of COmX510? If yes, can we use that data to generate dashboards in ComX510 for devices connected through EGX.
Yes...no problem
Also, is it possible to take a csv dump for all 40 devices from ComX510 at a regular interval (say every hour)?
Yes...no problem
I hope this helps,
James