Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ComX 510 stops displaying historical data and unable to export it

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • ComX 510 stops displaying historical data and unable to export it
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Romain_Polette Champion
128
Guillaume_Evrard
Guillaume_Evrard Leader
60
Randi_Dolan
Randi_Dolan Leader
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Maja555
Maja555
Explorer

Posted: ‎2023-10-29 07:28 PM . Last Modified: ‎2023-10-29 07:28 PM

0 Likes
1
1773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-29 07:28 PM

ComX 510 stops displaying historical data and unable to export it

Hello,

I have been troublehsooting a ComX 510 that suddenly stopped displaying (and exporting) logged data.  As you can see below this stopped suddently on the 29/08.

 

A remote power cycle did not resolve the issue.

 

Maja555_0-1698632574060.png

 

Devices are still set to log and no changes were made to cause the device to stop logging:

 

Maja555_1-1698632606431.png

 

Maja555_2-1698632616327.png

 

 

Periodic publication also stopped working some time ago. 

 

Attached is the diagnostic logs.

 

Help apprecaited,

 

Thanks 

Attachments
diagnostic.txt
oneesp.log
Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Romain_Polette Champion
Champion

Posted: ‎2023-11-07 05:05 AM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-07 05:05 AM

Hello @Maja555 , 

Is this the diagnostic log from your cloud application ? Or from the Com'X ?

 

Com'X log are normally encrypted and must be investigated by tech support Expert.

 

Please try at least to upgrade your Com'X to the last version (v6.8.7 year 2022) because your current application is very old (v3.0.7 year 2016).

  • https://www.se.com/ng/en/download/document/ComX_510_v6.8.7/

Regards, 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Reply 1
Romain_Polette
Romain_Polette Champion
Champion

Posted: ‎2023-11-07 05:05 AM

0 Likes
0
1729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-07 05:05 AM

Hello @Maja555 , 

Is this the diagnostic log from your cloud application ? Or from the Com'X ?

 

Com'X log are normally encrypted and must be investigated by tech support Expert.

 

Please try at least to upgrade your Com'X to the last version (v6.8.7 year 2022) because your current application is very old (v3.0.7 year 2016).

  • https://www.se.com/ng/en/download/document/ComX_510_v6.8.7/

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore