Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

ComX 510 "Undocumented Features"

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • ComX 510 "Undocumented Features"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
97
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2016-06-24 12:14 PM

1 Like
0
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-24 12:14 PM

ComX 510 "Undocumented Features"

We uncover a few ComX 510 "Undocumented Features."

1.  The Story:  Have a 510 that we want to us as a simple energy server for our new building in Menasha Wisconsin.  Other in our company decided to use Enercept meter to break out loads on      different floor and tenants.  You would think that the Enercept would be a native device to the gateway.  It is a Schneider product.  Nope, not on the list.  We need to make a custom driver for

     an existing, currently sold PowerLogic meter.

2.  We started by connecting an Enercept to the RS485 serial port.  We tested the connection by using the onboard diagnostics page.  Nothing returned and the device told us that the read was

     successful. mmmm....New firmware fixed this part. Nice that it can do "Floats" and not just integers. Note we did need to create a device.

3.  We were now seeing good data so we started building the custom read blocks and values.  Another glitch.  We were not getting the same values as we got when using the diagnostic page.      

     First we found that we had to start the BLOCK read at one less than the first register we needed.  Second we had to offset the register number by -1.

4.  To read a 32Float in holding register 259 we had to start our block read at 257 and ask for data in 258 to see what is in 259.

5.  This is odd since any the diagnostic page displayed the correct data by reading a block starting at 259.  How this device reads Modbus data is not consistent.  It is like the diagnostic page uses      Modus and the custom blocks use JBus.

6.  Please make us a native driver for the Enercept.  It is a PowerLogic Schneider meter.

7.  Since the device lets us create custom devices why can't they be shown in the monitoring tab?  Use the standard template and allow it to show any values that we create for a custom      device.  For values that we did not create or do not exist use ***** or other to show it does not exist.  I would think this would be nature to do.

Michael Franz

Technical Advisor

Faith Technologies

Tags (9)
  • Tags:
  • comx 510
  • custom devices
  • enercept
  • firmware
  • jbus
  • modbus master
  • off sets
  • rs-485
  • undocumented features
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now