Hello everyone,
When trying to connect to a Com'x 510 with my laptop for the first time, I plug the ethernet cable into both devices and the gateway appears on my computer network devices. But when I try to access it either through the IP in the browser or through the network devices, it can't connect.
Any suggestions would be much appreciated.
Best regards,
Pablo.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
I have also experienced this today. Brand new out of the box. Customer cannot open com X 510 log on screen. The Com X icon is displaying under network tab, but we get a cannot connect error every time. have tried;
1. Rebooting laptop and com x
2. Changing Ethernet lead
3. Tried eth ports 1 and 2
4. Upgraded firmware to 3.6.3
5. using IPv4 connection
Please can anyone assist as I need to get this working by tomorrow.
Link copied. Please paste this link to share this article on your social media post.
Just solved issue.
Factory reset (Push 2 front buttons and hold 10 seconds while powering on).
Now logs on via IPV6