Com'X510 Firmware 1.1.44 Exhibites Errors When Integrating with PM8000

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X510 Firmware 1.1.44 Exhibites Errors When Integrating with PM8000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
KuanKhoon
Lt. Commander KuanKhoon Lt. Commander
Lt. Commander

Posted: ‎2015-08-06 08:36 PM

0 Likes
5
1761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-06 08:36 PM

Com'X510 Firmware 1.1.44 Exhibites Errors When Integrating with PM8000

Good Morning,

We have just executed a firmware upgrade of the Com'X510 on testing and integrated to a PM8244. The displayed power readings are 1000 times the correct value, the THDi and THDv readings are missing and on a side note the decimal points for the voltage readings are not displayed either.

The hardware and firmware version of the Com'X510 as below,

Application version          1.1.44

MCU board FW version   2.2.6

Root Partition version      4.1.7

Soft Partition Version      1.1.44

Hardware version            5

The screen capture pf the Com'X510 as below,

7168

The screen capture of the PM8000 webpage showing the correct power readings,

7174

The screen capture of the PM8000 webpage showing the presence of the THDv and THDi values,

7173

Tags (3)
  • Tags:
  • 1.1.44
  • comx510
  • pm8000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-08-07 07:13 AM

0 Likes
1
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-07 07:13 AM

Hi Randi/team,

Can you please take a look at this one.  Is this expected?

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2015-08-07 08:59 AM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-07 08:59 AM

Hi John/James.

It looks like this is a problem with the way the PM8000 reports Modbus Values.  The Register List states that the Modbus value reported is in kW (or kVAR or kVA).  These values are 1000 times what is displayed on the meter display.

7175

The display on this unit reads

1.443 kW

James/John - Do you agree this is an issue with the PM8000?

Thanks,

Randi

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2015-08-10 08:48 AM

0 Likes
2
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-10 08:48 AM

Hi,

Thank you for bringing this to our attention.  We have notified the PM8000 Continuous Engineering Team about the scaling issue with the Power Readings.


The Com'X 510 shows values that are displayed as a percentage in the PM8000 as raw data (not a percent).  So, for the Power Quality Readings. some values are too small to display correctly in the Device Settings Measurements table.  These values are displayed as a percentage in other areas of the user interface, such as the Real Time Readings.  We do plan on making the display of these values consistent in a future release.


Thanks again for bringing this to our attention.


Randi

Reply
KuanKhoon
Lt. Commander KuanKhoon Lt. Commander
Lt. Commander

Posted: ‎2015-08-28 10:04 PM

0 Likes
1
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-28 10:04 PM

Hi Randi,

I just drilled deeper the PM8000 modbus register list. There is documentation for register 3060 (Active Power Total), 3068 (Reactive Power Total) and 3076 (Apparent Power Total). All the registers at type FL32 and all units are in W, VAR and VA. Can you check that you are using the correct Modbus register list for the production version of PM8000? The modbus register list I have is "Release 1 FW" and I have copied you in the attachment

7339

Best Regards,

Kuan Khoon

Attachments
Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2015-08-30 08:34 PM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-30 08:34 PM

Hi Kuan,

You are correct.  The register list I was working off of was a bit confusing since it contained all of the meters using the PMC Register List.  I was informed by the PM8000 development team that they use "PDM Compliant" units.  We have corrected this in the Com'X and it will be available in a future release.

Thanks for finding this issue and following up with it.

Please let me know if there is anything else we can help you with.

Randi

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.