Com'X510 - Connection loss and endless reboot

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X510 - Connection loss and endless reboot
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
Romain_Brunner
Ensign Romain_Brunner Ensign
Ensign

Posted: ‎2018-03-12 12:24 AM

0 Likes
10
2192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-12 12:24 AM

Com'X510 - Connection loss and endless reboot


Hi all,

We installed 14 Com'X510 in metro stations for a public transportation customer.

From the beginning of the project we experienced several issues, but two did occur more often than others:

- Unplanned reboot of the Com'X that never ends. We only get to the "The box is starting" page and that's it

- Total connection loss with the Com'X. The IP address doesn't answer anymore.

All boxes are on the same network, some have the 3.6.3 firmware, other the 4.0.10. It doesn't seem to change anything.

We have a VPN access on the network, but it isn't very useful in these two cases. We need to go on site to reboot the Com'X, knowing that it can happen again because the cause is unknown. Moreover, we need at least 5 days to get an authorization to go on site, so the customer is becoming very angry and begins questioning our products.

I have really no clue about what is going on there. As it is the only project where we have such problems, I'm beginning to think it can be network related.

Do someone experience a similar issue, or have any suggestion?
As we are forced to

Tags (4)
  • Tags:
  • com x 510
  • diagnostic
  • reboot
  • troubleshooting
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
Anonymous user
Not applicable

Posted: ‎2018-03-12 12:32 PM

0 Likes
9
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-12 12:32 PM

Hi Romain,

I'm very sorry to hear you are having these issues. Can you help us with some more information on these ComX:

  • In v4.0.10, we've fixed some issues specific to the ComX continually starting. Can you confirm you have seen this issue also on ComX with 4.0.10?
  • How many devices do you have configured in each ComX?
  • What network method is the ComX using (ethernet, cellular, etc)?
  • How many ComX have you seen these issues on?
  • Does a reboot of the ComX fix both issues?


Best Regards,

Colton

Reply
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2018-03-13 05:54 AM

0 Likes
7
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-13 05:54 AM

Hi Colton,

I think I might have reproduced the issue on my test Com'X510 - the IP address of Eth1 has changed, but the Data Logger is still uploading files to FTP server. Let me know if you need more information in order to reproduce the bug:

Mar 6. ComX'510 had IP: 192.168.0.23 and it was "pingable" from FTP server.

Mar 13. ComX'510 has IP: 196.254.11.164 an it is not "pingable" any more, but it uploads data logs for FTP server regularly:

Reply
Anonymous user
Not applicable

Posted: ‎2018-03-13 06:01 AM

0 Likes
6
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-13 06:01 AM

Hi Bojan,

Is your ComX configured to be in DHCP mode? This could be some sort of IP address conflict.

Best,

Colton

Reply
Anonymous user
Not applicable

Posted: ‎2018-03-13 06:16 AM

0 Likes
5
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-13 06:16 AM

Hi Bojan,

The IP address you are seeing your ComX revert to: 169.254.x.x is a "ZeroConf" address. This means that for some reason the ComX was unable to get an IP address assigned by the DHCP server. This is almost certainly a network issue. To eliminate the DHCP server as a problem, can you try setting the ComX into static IP mode?

Best,

Colton

Reply
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2018-03-13 08:09 AM

0 Likes
4
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-13 08:09 AM

Hi Colton,

It looks like there was a problem with ComX renewing the lease.

It should have tried to renew it's lease when 50 percent of the lease time has expired. To renew its lease, ComX  DHCP client should have sent a DHCPRequest message to the DHCP server from which it originally obtained the lease.

It looks like it have never happened, so I manually unplugged Ethernet cable from Eth1 and plugged it back and  everything is back to normal now.

I'm wondering if that was the Romain's issue in loosing IP addresses, too?

Reply
Anonymous user
Not applicable

Posted: ‎2018-03-13 08:12 AM

0 Likes
1
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-13 08:12 AM

Hi Bojan,

The scenario you described would certainly explain how your ComX ended up in a ZeroConf state. Can you share your diagnostic information for how you determined the DHCP client did not request the new IP address?

Best,

Colton

Reply
Romain_Brunner
Ensign Romain_Brunner Ensign
Ensign

Posted: ‎2018-03-13 08:59 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-13 08:59 AM

Hi Colton,

To answer your questions:

  • In v4.0.10, we've fixed some issues specific to the ComX continually starting. Can you confirm you have seen this issue also on ComX with 4.0.10?
    • The box continually starting has the 3.6.3 firmware. The box not responding has the 4.0.10 one. I would say that the starting problem occurs only with 3.6.3 but I can't be 100% sure.
    • The thing is that these Com'X originally published csv files by email, and we got some problems with the 4.0.10 for this function (impossible to change the recipients list, impossible to save some publication parameters), so we kept them on 3.6.3.
  • How many devices do you have configured in each ComX?
    • Between 1 and 3
  • What network method is the ComX using (ethernet, cellular, etc)?
    • All are on ethernet
  • How many ComX have you seen these issues on?
    • 4
  • Does a reboot of the ComX fix both issues?
    • Yes, but only temporarily

Hope it can help you.

Thanks for your help,

Romain

Reply
Romain_Brunner
Ensign Romain_Brunner Ensign
Ensign

Posted: ‎2018-03-13 09:02 AM

0 Likes
1
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-13 09:02 AM

Hi Bojan,

In our issue, the Com'X doesn't publish on the FTP anymore, that's how we identified the malfunction.

I don't know what renewing the lease means. Can you explain me?

Thanks,

Romain

Reply
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2018-03-13 09:36 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-13 09:36 AM

Hi Colton,

Here is my diagnostics file.

I can only wait one week for lease to expire and confirm the issue.

Best regards,

Bojan

Reply
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2018-03-13 09:45 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-13 09:45 AM

Hi Romain,

You can find more about the renewing the lease in this article.

It's not relevant to your project if you set the ComX into static IP mode. It applies to DHCP mode only.

Best regards,

Bojan

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore