COM'X floating Point Registers

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • COM'X floating Point Registers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
Andy_Hubert
Lieutenant Andy_Hubert Lieutenant
Lieutenant

Posted: ‎2021-06-25 03:42 AM

0 Likes
8
1710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-25 03:42 AM

COM'X floating Point Registers

Hi,

 

I have a customer who is using a number of COMX 210s to count pulses from WAGES devices.

 

The device type only has integer type registers for the cumulative usage, whereas the device shows a value with decimal places.

 

The only floating point registers I can find in the manual are for the raw count value, this would mean us having a bespoke device type for each of the COMX devices, where we then add any offsets, and do the scaling.

 

Obviously it is easiest to do the scaling and offsets in the COMX, that way we only need one device type, and we have a better method of comparing PME with the value at the device.

 

Do registers with floating point values for the Cumulative usage exist?? and if so where do I find them?

 

Thanks

 

Andy

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2021-06-29 05:10 AM

0 Likes
6
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-29 05:10 AM

Hi Andy,

 

Is the customer using the onboard Digital Inputs?  If so, the register defined starting at page 120 in the User Manual are the registers that are available for the inputs.

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=ComX210UserManual_D...

 

Randi

Tags (1)
  • Tags:
  • english
Reply
Andy_Hubert
Lieutenant Andy_Hubert Lieutenant
Lieutenant

Posted: ‎2021-07-21 07:23 AM

0 Likes
5
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-21 07:23 AM

Hi,

 

we are using digital inputs, in the COM'x we can configure scaling, and in the web pages we get a scaled value that will show decimal places, but the registers are integers so this is lost when we view the register values in PME.

 

Regards

 

Andy

Tags (1)
  • Tags:
  • english
Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2021-07-21 07:49 AM

1 Like
4
1698
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-21 07:49 AM

Hi Andy,

 

The Com'X scales the pulse counts using the pulse weights and offset to calculate "Energy" and "Instantaneous Power".  These are represented in the register list as "Measured Value" and "Measured Flow", respectively.

 

Best regards,

Randi

Tags (1)
  • Tags:
  • english
Reply
Andy_Hubert
Lieutenant Andy_Hubert Lieutenant
Lieutenant

Posted: ‎2021-09-02 06:50 AM

0 Likes
3
1692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-02 06:50 AM

Hi,

 

I have had a look through the register list again, and can see that the 'Pulse weight', 'Measured Flow are floating point numbers, but the 'Pulse Count' registers, and the 'Measured Value' registers are integers.

 

This means that the value is scaled and has an offset added, and you can see this in the Com'x, but the value in PME is only the Integer.

 

i.e 

 

COM'x Value 2.35 m3

PME Value 2 m3

Tags (1)
  • Tags:
  • english
Reply
Olivier_GARAULT
Lieutenant JG Olivier_GARAULT Lieutenant JG
Lieutenant JG

Posted: ‎2021-09-02 08:18 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-02 08:18 AM

Hello Andy,

I have some knowledge of Com'X 510 commissioning but I don't have the answer to your question.
sorry
Olivier

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2021-09-02 08:35 AM

0 Likes
2
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-02 08:35 AM

Hello @Andy_Hubert , 

 

The ComX_Wage PME driver is based on the Com'X Modbus Map.

 

I checked the driver and it matches exactly.

 

So it seems we have not the choice.
ComX web page will display a floating point, and PME will display / log an integer.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2021-09-02 08:42 AM

0 Likes
1
1682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-02 08:42 AM

@Andy_Hubert 

 

Can you try to change the "Cumulative Usage" Display Resolution from 0 to 2 under the ComX_Wage Vista Diagram ?

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Andy_Hubert
Lieutenant Andy_Hubert Lieutenant
Lieutenant

Posted: ‎2021-09-03 02:31 AM . Last Modified: ‎2021-09-03 02:40 AM

0 Likes
0
1677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-03 02:31 AM

Hi,

 

This doesn't have any effect, as the register is an integer, and therefore cannot have any decimal places.

 

Is there any way we can get the scaled values into a floating point register in a new firmware version??

 

Thanks 

 

Andy

 

 

Web page ViewWeb page ViewPMEPMEPME LogPME Log

Tags (1)
  • Tags:
  • english
Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore