COM'X 510 unable to update via USB and still power LED orange.

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • COM'X 510 unable to update via USB and still power LED orange.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
The_power_sniffer
Crewman The_power_sniffer
Crewman

Posted: ‎2024-01-10 01:18 AM

0 Likes
8
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-10 01:18 AM

COM'X 510 unable to update via USB and still power LED orange.

Dear All , 

I know com'x is a legacy by now device. 
But I am unable to update it from the front USB port. 
I tried several versions and several USB sticks and nothing it just hangs. 
I would like to know if there is a way to connect via SSH and update it the hard way ? 
Thank you in advance 

 

The power Sniffer. 

Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-01-10 11:34 PM

0 Likes
0
1687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-10 11:34 PM

Hi @The_power_sniffer , 

Unfortunately you cannot do anything because your Com'X did not start after many hours.

Then upgrade is not possible.

 

You can try to factory reset your Com'X (all data and configuration will be lost). Even if after a factory reset, your Com'X cannot be recovered, you will need to contact your local tech support.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 8
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-01-10 04:30 AM

0 Likes
1
1711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-10 04:30 AM

Hello @The_power_sniffer , 

If your Com'X510 Power LED is in steady orange state, it means that your device power up process is still on going. The more devices you added to your Com'X, the more time needed to boot up. During start up, you cannot do anything on the Com'X.

 

Did you wait 1 hour to check if the Power LED switches to green ? Did you power off/on your Com'X ?

If your Com'X is still in steady orange state, something is wrong and this must be checked with tech support (support is limited for this device).

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
The_power_sniffer
Crewman The_power_sniffer
Crewman

Posted: ‎2024-01-10 07:05 AM

0 Likes
0
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-10 07:05 AM

it never changes status even after months.
is there any other way to find out the status of the OS on the device ?
Thanks

Reply
The_power_sniffer
Crewman The_power_sniffer
Crewman

Posted: ‎2024-01-10 07:39 AM

0 Likes
0
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-10 07:39 AM

Dear Miss @Romain_Polette 

Yes unfotunatlly after 1 hour the light is still orange. 

UPS upgrade does not work and the only thing I can find is the SSH server no WEB server avalable. 

I would like to know if there are limitations to formatting and size , and USB2 vs USB 3 connection for the memory stick 

If it would be possible to get such info it would be lovely. 


Thanks 


Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-01-10 11:34 PM

0 Likes
0
1688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-10 11:34 PM

Hi @The_power_sniffer , 

Unfortunately you cannot do anything because your Com'X did not start after many hours.

Then upgrade is not possible.

 

You can try to factory reset your Com'X (all data and configuration will be lost). Even if after a factory reset, your Com'X cannot be recovered, you will need to contact your local tech support.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
The_power_sniffer
Crewman The_power_sniffer
Crewman

Posted: ‎2024-01-11 03:34 PM

1 Like
0
1670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-11 03:34 PM

Dear @Romain_Polette 

After Factory reset the comx funally worked. I manage to update the FW too. So all is good. 

I would like to also know if its possible to get an aftermarket ZigBee dongle ? because I am unable to find the original one. 

Thanks 

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-01-11 11:41 PM

0 Likes
1
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-11 11:41 PM

Hi @The_power_sniffer , 

It will be very difficult to find the ZigBee dongle because this device was removed from market many years ago. This dongle was not very reliable with PowerTag and many communication issues with EM4300.

 

Do you have some Zigbee meters connected to your Com'X ?

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2024-01-14 08:44 PM

1 Like
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-14 08:44 PM

hello @The_power_sniffer ,

If you have TH/CL connected using the dongle, you might try this : 

REL52867,

Only doubt is the FW loaded on the dongle.

I did not check but normally the Fw should be updated by the ComX upon initialization, not guaranted but you might try...

 

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-01-16 12:31 AM

0 Likes
0
1620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-16 12:31 AM

Hi @Guillaume_Evrard , 

Good catch 🙂 I was not aware this ZB dongle survived through another offer.

 

You are right, normally the EBXA-USB-ZIGBEE is aligned with the Com'X FW and upgraded when you plug the dongle and power on the Com'X:

Romain_Polette_0-1705393585389.png

 

What I cannot tell if the commercial ref REL52867 is fully compatible with the Com'X. Design seems the same, but FW inside REL52867 may not be recognized by the Com'X FW.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore