BSCM Modbus SL EPC discovery

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • BSCM Modbus SL EPC discovery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
113
Guillaume_Evrard
Captain Guillaume_Evrard Captain
55
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All
Related Products
product field
Schneider Electric
ComPact NSX

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
jedzruiz1985
Lieutenant JG jedzruiz1985
Lieutenant JG

Posted: ‎2025-10-07 10:47 PM

0 Likes
6
175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-07 10:47 PM

BSCM Modbus SL EPC discovery

Hi Xperts,

 

Need help!

 

Just want to know the correct steps on how to commission an NSX breaker with ML6 that has a BSCM Modbus/SL (LV434220) connected to a Modbus SL hub LV434224) via BSCM SL cord (LV434223) and connected to an IFE server (LV434002) via stacking connector TRV00217.

 

The trip unit is working however we cannot discover the breaker from the IFE Server. We set the rotary switch to position 0 so we can address them using EPC. Do you have a step by step procedure on how to correctly do this since we are trying to discover it using EPC but unfortunately cannot.

 

jedzruiz1985_0-1759902321725.png

 

jedzruiz1985_1-1759902329313.png

 

Thanks in advance,

 

Jedz

  • Thumbnail of ComPact NSX
    Schneider Electric
    ComPact NSX
View products (1)
Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-10-08 10:27 PM

1 Like
0
149
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-08 10:27 PM

Hello @jedzruiz1985 ,

Personnaly I am never using 0, I set the modbus Id using the switch.

If you connect to the modbus interface of the IFM using a RS485 converter it will work, we are doing it for other serial modbus devices.

Kind Regards

See Answer In Context

Reply
Replies 6
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-10-08 01:37 AM . Last Modified: ‎2025-10-08 02:39 AM

0 Likes
0
164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-08 01:37 AM

Hello @jedzruiz1985 , 

When you press the "Mode" button (5 sec) in the front face of your Micrologic 6.xE, what is the address "Adxx" displayed ?

 

Can you confirm you have no duplicate addresses on all your Micrologic 6.xE ?

 

I tested with a Panel Server + 2x Micrologic 5.2E and when BSCM is set to '0', the modbus ID displayed on the micrologic is "Ad99" for both Micrologic. So I suppose EPC or IFE detects duplicate Modbus ID and blocks the discovery process.

 

I'm not an expert with EPC, but it seems that the software cannot automatically attribute Modbus ID to the BSCM. 

 

If you read the IS:

Romain_Polette_0-1759915154747.png

 

According to the User Manual:

Romain_Polette_1-1759915277540.png

=> you will need an USB to serial RJ45 adapter like TSXCUSB485 to communicate directly in serial with the Modbus Hub.

 

Workaround I tested: force the Modbus ID from the Micrologic trip unit front face:

  1. Press mode 5 sec (you will see the current Modbus ID)
  2. unlock the Micrologic (hope the trip unit is not sealed)
  3. set Modbus ID with up/down arrow
  4. Press OK button 2 times

You opened a tech support ticket, so I will let the EPC support answer.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
jedzruiz1985
Lieutenant JG jedzruiz1985
Lieutenant JG

Posted: ‎2025-10-08 08:34 PM

0 Likes
1
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-08 08:34 PM

Hi Romain,

 

We are benchmarking it as well here on our end. Same solution ended up with yours. Need to change the addresses in the trip units first otherwise they will fight over id 99.

 

You can only change the ID using EPC. Still you need to set it on the trip unit first before it can even discover it. What we did not tried yet is if it is possible without the IFE server to discover the breaker from the modbus hub SL directly as per the publication. Otherwise the publication needs to be revised. It is misleading.

 

While you are at it... can you try combinations of using IFM with the new BSCM and IFM with old BSCM and one in a Modbus SL Hub with new bscm. Can you please bench test it if it will work properly?  Raised this just in case retrofits are required on site in the future.

 

Regards,

 

Jiedan

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-10-08 10:27 PM

1 Like
0
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-08 10:27 PM

Hello @jedzruiz1985 ,

Personnaly I am never using 0, I set the modbus Id using the switch.

If you connect to the modbus interface of the IFM using a RS485 converter it will work, we are doing it for other serial modbus devices.

Kind Regards

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-10-09 01:30 AM . Last Modified: ‎2025-10-09 01:40 AM

3 Likes
0
141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-09 01:30 AM

Hello @jedzruiz1985 , 

 

Please update your tech support ticket if our answers are OK for you.

 

"Otherwise the publication needs to be revised. It is misleading."

=> I Agree. This could be "annoying" when you installed many NSX with new BSCM with factory settings and want to set it up remotely with EPC. 

 

"While you are at it... can you try combinations of using IFM with the new BSCM and IFM with old BSCM and one in a Modbus SL Hub with new bscm. Can you please bench test it if it will work properly?"

=> IFM + new BSCM: you need to use the ULP port of new BSCM connected to IFM ULP port. So you need to set the Modbus ID on the IFM front face (rotary switches). In this case, this is not possible to change the Modbus ID with EPC or with Micrologic screen.

=> IFM + old BSCM: same as above. Modbus ID must be set on IFM.

=> Modbus Hub + new BSCM : Only compatible with Modbus port of the new BSCM module. You can set the Modbus ID with rotary switch (limited to 13 IDs) or with Micrologic 5/6/7 screen when rotary switch is set to '0'. You can also use EPC as discussed above, but only to set up 1 breaker Modbus ID. Not possible to set up multiple NSX at the same time when BSCM is in factory config.

=> Modbus Hub + old BSCM : Forbidden 🙂

 

You can stack :

  • Modbus Hub + IFM + IFE .
  • Modbus Hub + IFM and then connect a Panel Server

Please read this interesting section of the updated ULP Guide:

https://www.productinfo.schneider-electric.com/ulp_system_guide/doca0093-ulp-system-user-guide/Engli... 

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-10-09 09:58 PM

0 Likes
0
123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-09 09:58 PM

Thanks a lot @Romain_Polette for the full explanation basically Old BSCM = only ULP and new BSCM ULP and Modbus.

Reply
jedzruiz1985
Lieutenant JG jedzruiz1985
Lieutenant JG

Posted: ‎2025-10-13 12:47 AM

0 Likes
0
49
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-13 12:47 AM

Has anyone tried the new solution if it really works seamlessly if there are multiple SL hubs and breakers? I don't have the gears with me unfortunately to try it out. Hopefully you guys can simulate and confirm if the status indications "open, close and trip" are operating properly. Raising this since I have previously had a switchboard that has this when this setup was newly released and can't seem to get the correct status indications on the breakers so we had to revert back to the old architecture using the ifms and the old bscm which worked properly as expected.

 

Thanks

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore