Automatic contactor control based on current

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Automatic contactor control based on current
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
57
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
kuon
kuon
Cadet

Posted: ‎2023-01-17 05:49 PM

0 Likes
2
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-17 05:49 PM

Automatic contactor control based on current

I found your powertag current sensor line and I found them to be cost effective and easy to install. Now, I am a bit lost in the different "gateways" you have.

 

I found the PowerTag link which seems to be now obsolete so I don't know what the replacement should be.

 

Basically, here is what I need:

 

- Ability to read current sensors via the network (Modbus IP or SNMP)

- Ability to control contactors when current threshold is reached

 

I think the first item is not a problem, but I didn't find any device that could do the second one.

 

The idea is to have current sensors on solar and different power users, and based on different condition like this:

 

- if solar power > used power + 3kw, turn on contactor A.

- if solar power > used power (now including the current sensor from contactor A) + 7kw, turn on contactor B.

...

 

 

Labels
  • Labels:
  • Product selection
Tags (2)
  • Tags:
  • english
  • powertag
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-01-17 11:43 PM

0 Likes
0
1173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-17 11:43 PM

Hello @kuon , 


When developing new project with PowerTag sensors, you need to use the Panel Server. PowerTag Link is no more commercialized 

 

Regarding your needs:

  1. Ability to read current sensors via the network (Modbus IP or SNMP)
    • Panel Server can read all measurements from a PowerTag Sensor
    • SNMP is not available in the Panel Server, but you can read the Modbus Registers of the PowerTag Sensors through Modbus TCP (Panel Server as a gateway)
  2. Ability to control contactors when current threshold is reached:
    • Panel Server do not embed threshold management with control
    • You will need a system upstream your Panel Server to control some contactors depending on a threshold (PLC, Software).
    • For better integration, you can use Panel Server + Smartlink Modbus IO channels + Schneider contactor with 24DC relay
    • You can also use Panel Server only to read PowerTag Sensors values from a PLC, and integrate control in the same PLC.

Regards, 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 2
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-01-17 11:43 PM

0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-17 11:43 PM

Hello @kuon , 


When developing new project with PowerTag sensors, you need to use the Panel Server. PowerTag Link is no more commercialized 

 

Regarding your needs:

  1. Ability to read current sensors via the network (Modbus IP or SNMP)
    • Panel Server can read all measurements from a PowerTag Sensor
    • SNMP is not available in the Panel Server, but you can read the Modbus Registers of the PowerTag Sensors through Modbus TCP (Panel Server as a gateway)
  2. Ability to control contactors when current threshold is reached:
    • Panel Server do not embed threshold management with control
    • You will need a system upstream your Panel Server to control some contactors depending on a threshold (PLC, Software).
    • For better integration, you can use Panel Server + Smartlink Modbus IO channels + Schneider contactor with 24DC relay
    • You can also use Panel Server only to read PowerTag Sensors values from a PLC, and integrate control in the same PLC.

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
kuon
kuon
Cadet

Posted: ‎2023-01-18 03:18 AM

0 Likes
0
1168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-18 03:18 AM

Thank you for your quick answer.

 

I wanted to avoid having an additional component for trigger management to reduce cost.

 

I guess I'll have to add a controller.

 

Best regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore