EcoStruxure IT Gateway 1.8.1 and newer include more accurate device support for the Uniflair family of CRACs and chillers. With these additions to the Gateway device library, you will need to do a targeted discovery in EcoStruxure IT Gateway.
If you have previously discovered Uniflair devices, and have updated to Gateway 1.8.1, you must delete previously discovered Uniflair devices and then rediscover them. Existing device data will not be preserved. See a list of affected devices in the EcoStruxure IT Gateway 1.8.1 release notes
Uniflair devices discovered in Gateway 1.8.1 or later are not affected.
Follow these steps to discover your Uniflair device:
SNMP Discovery
Enter the IP address of the device you want to discover.
GW18_Uniflair_discovery_1_360006532378.png
When the discovery finishes, you'll see this message:
GW18_Uniflair_discovery_2_360006532378.png
Click Choose device type to see a list of available device types, for example, Chiller or CRAC .
GW18_Uniflair_discovery_3_360006532378.png
Select the vendor Uniflair.
GW18_Uniflair_discovery_4_360006532378.png
You'll see a list of all the available device support files for your selection, Uniflair Chiller in this example.
GW18_Uniflair_discovery_5_360006532378.png
This is a partial list of the Uniflair chillers. To determine which file is correct for your device, you need more information:
The full model name of the device, for example, ERAF1221A.
The PLC (programmable logic controller) and HMI (human-machine interface) your device is equipped with.
When you have this additional information, you can break down the file names and select the proper one.
Let's use an ERAC1221A equipped with a pCO5+ PLC and a UG50 HMI as an example.
The first part of the file name is the model name, followed by the model number (with x as a wildcard). You know it will be Erac_xx21a, but there are 2 files that start with that combination. That's why you need to know which PLC and HMI are equipped.
IMPORTANT: Devices with the same model name but a different PLC/HMI are NOT compatible.
The correct file for this device is Erac_xx21a_pco5_plus_ug50_metric. If you selected Erac_xx21a_pco1_ug40_metric instead, measurements in EcoStruxure IT will be inaccurate,
Modbus Discovery
Modbus discovery is similar to previous Gateway versions. There is a list for Type, Vendor, and Family (DDF name). The file names are structured the same as in step 5 of the SNMP discovery section. Enter the IP address and server address and select Discover Modbus device.
GW_Uniflair_discovery_2020_360006532378.png
Note: Modbus.org announced it is expunging all occurrences of inappropriate language of the query and response paradigm of Modbus communications. More...