IT Expert - Device not recognized
ITE Configuration
Detailed instructions for how to configure EcoStruxure IT Expert
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
When the device status is Device not recognized or Device not ready in IT Expert, it is usually because the device IP address was reused, or the device is not configured properly in the Gateway.
Common reasons for failure
Resolution
The device replaced an older device.
Remove the old device in the Gateway, and then discover the new device. It is important that the old offline device is removed from the Gateway before you discover the new device. How to replace a device in EcoStruxure IT Gateway
The device IP address was reused.
Make sure the IP address for the device is not being used by any other device in IT Expert. Go to Devices and type the IP address into the search bar.
Make sure the Gateway does not have any other devices registered with that IP address. If there are devices using the same IP address, remove the old device(s) and then rediscover the new one. How to replace a device in EcoStruxure IT Gateway
The device is on the wrong port.
Make sure port settings are correct on the device and in the in the Gateway.
IMPORTANT: After you make any changes to devices in the Gateway, you must rediscover the affected devices.
Some EcoStruxure IT features may not work properly when device IP addresses are not configured correctly.