the difference between IEC 61000-3-12 and IEEE519

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • the difference between IEC 61000-3-12 and IEEE519
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Power Distribution and Digital Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Expert on Demand for Standards & Regulations
Start a Topic
Widiyatmoko
Ensign Widiyatmoko
Ensign

Posted: ‎2022-02-24 01:12 AM

0 Likes
6
8470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-24 01:12 AM

the difference between IEC 61000-3-12 and IEEE519

Please share more on IEC 61000-3-12? And what is the difference between IEC 61000-3-12 and IEEE519?

Initially, I have the impression that IEC 61000-3-12 is observing a THDI of 5%.

@HelvinHermanT 

 

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-02-24 10:25 PM

0 Likes
5
8455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-24 10:25 PM

Hi Pak,

 

The International Standard IEC 61000-3-12 has been prepared by subcommittee 77A: Low frequency phenomena, of IEC technical committee 77: Electromagnetic compatibility.

 

IEC 61000-3-12 Part 3-12: Limits – Limits for harmonic currents produced by equipment connected to public low-voltage systems with input current >16 A and ≤75 A per phase.

 

This part of IEC 61000 deals with the limitation of harmonic currents injected into the public supply system. The limits given in this International Standard are applicable to electrical and electronic equipment with a rated input current exceeding 16 A and up to and including 75 A per phase, intended to be connected to public low-voltage a.c. AC distribution systems of the
following types:
• nominal voltage up to 240 V, single-phase, two or three wires;
• nominal voltage up to 690 V, three-phase, three or four wires;
• nominal frequency 50 Hz or 60 Hz.
Other distribution systems are excluded. The limits given in this edition apply to equipment when connected to 230/400 V, 50 Hz systems

 

NOTE 1 The limits for the other systems will be added in a future edition of this standard.
NOTE 2 Equipment with a rated input current exceeding 75 A per phase should be considered in the harmonic current requirements for installations. See IEC/TR 61000-3-6 and future IEC/TR 61000-3-14.

 

This standard defines:
a) requirements and emission limits for equipment;
b) methods for type tests and simulations.
Tests according to this International Standard are type tests of complete pieces of equipment.
Conformity with this standard can also be determined by validated simulations

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-02-24 10:31 PM . Last Modified: ‎2022-02-24 10:35 PM

In response to HelvinHermanT
0 Likes
2
8452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-24 10:31 PM . Last Modified: ‎2022-02-24 10:35 PM

The limits given apply to 230/400 V, 50 Hz systems. The limits for the other systems will be added in a future edition of this standard.

 

The harmonic current limits specified in the tables apply to each of the line currents and not to current in the neutral conductor.

 

The harmonic current limits are specified in Tables.

 

Tabel 3 IEC 61000_3_12_2011.jpg

 

Please note that the data above is just for reference only. Please check the complete Standard for better understanding. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2022-02-28 05:59 AM

In response to HelvinHermanT
0 Likes
0
8441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-28 05:59 AM

 
Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
Reply

Link copied. Please paste this link to share this article on your social media post.

J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2022-02-28 05:59 AM . Last Modified: ‎2025-08-11 04:13 AM

In response to HelvinHermanT
1 Like
0
8441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-28 05:59 AM . Last Modified: ‎2025-08-11 04:13 AM

Hello @Widiyatmoko ,

 

I took the initiative to post your question into our Global Community:

 

"Power Distribution & Digital forum"

 

We got an answer from @DGonzalez to complement the discussion above.

I hope it will help. 

 

You can check it out here. 👈 👈

 

 

Capture.JPG

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sesa72599_bridg
sesa72599_bridg Cadet
Cadet

Posted: ‎2024-06-04 03:11 AM

In response to HelvinHermanT
0 Likes
1
4854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-04 03:11 AM

Hi

Thanks for the explanation. By any chance, do you have an IEC 6100 Electromagnetic Test Report for our USB charging units?

Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2024-06-26 05:49 AM

In response to sesa72599_bridg
0 Likes
0
4705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-26 05:49 AM

Hi, please contact your local Offer Marketing Manager. 🙏

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore