Update info Panel Tengangan 24KV

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Update info Panel Tengangan 24KV
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Power Distribution and Digital Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
CitraR
Ensign CitraR
Ensign

Posted: ‎2022-05-17 12:29 AM

0 Likes
3
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 12:29 AM

Update info Panel Tengangan 24KV

Mohon informasi update informasi untuk Panel Tengangan 24KV, apa saja offer yang dapat diberikan oleh Schneider ?

 

Jika ingin breaking capacity yang 25kA, apakah tersedia ada ?

 

Mohon diberikan informasinya.

Labels
  • Labels:
  • Indonesia
  • Tags:
  • bahasa Indonesia
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
Lieutenant JG

Posted: ‎2022-05-17 12:57 AM

2 Likes
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 12:57 AM

Hello 

 

Di schneider panel Primary 24kV mulai dari 25kA, 31,5kA dan 41,5kA

Switchgear 24kV 25kA juga terbagi atas :

1. Gas Insulated Switchgear beberapa product nya adalah GHA, WSB, CBGS dengan rating current mulai dari 630A sampai 4000A

2. Air Insulated Swichgear 24kV 25kA ada beberapa type product MCSET 4 untuk Switchgear dengan CB menggunakan Gas SF6 dan PIX24 untuk pilihan menggunakan CB Vacuum

 

productnya merupakan Engineering To Order (ETO) dibuat berdasarkan kebutuhan dan spesifikasi khusus menyesuaikan kebutuhan 

 

info lebih lanjut bisa di lihat dalam tautan berikut ini 

 

https://www.se.com/ww/en/product-subcategory/87898-primary-air-insulated-switchgear/ 

https://www.se.com/id/en/product-subcategory/87901-primary-gas-insulated-switchgear/

 

silahkan menghubungi sales schneider lebih lanjut untuk product yang diperlukan bila ini adalah sebuah extension atau perlu adanya modifikasi silahkan menghubungi saya dari team service untuk support lebih lanjut 

 

salam 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

faisalamir
Lieutenant faisalamir Lieutenant
Lieutenant

Posted: ‎2022-05-17 01:51 AM

2 Likes
0
1349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 01:51 AM

Hi Citra,

 

Menambahkan informasi dari rekan-rekan sebelumnya terkait pertimbangan dan pemilihan tipe panel tegangan menengah (panel TM)

 

Maka beberapa informasi dibawah ini perlu diketahui sebagai bagian dari basis data teknis untuk pemilihan tipe panel:

 

 1. Tipe panel TM menggunakan Isolasi Udara (AIS=Air Insulated Swicthgear) atau menggunakan Gas SF6 (GIS=Gas Insulated Switchgear =Fully Insulated Switchgear)?

untuk tipe panel Schneider saat ini baik AIS dan GIS sudah ada opsi dengan menggunakan teknologi yang menggantikan gas SF6 sebagai media breaking capacity dan media Isolasi Dielektrik 

 

2. Info mengenai tegangan, frekuensi, dan kemampuan hantar arus normal terus menerus (KHA)

 

3. Info mengenai tingkat ketahanan arus hubung singkat berikut durasi hubung singkat (dalam detik) 

 

4. Info sistem grounding berikut dengan arus ketahanan gangguan fase-bumi

 

5. Indeks pengaman selangkup dan partisi

 

6. Info mengenai kelas untuk Loss of Service Continuity (LSC1 atau LSC2) dan Partitioning (PM or PI) mengacu pada standard IEC 62271-200

 

Untuk memudahkan pemilihan produk panel TM secara otomatis di web schneider dapat diakses di link berikut:

https://www.se.com/ww/en/product-category/87897-medium-voltage-switchgear/?filter=business-6-medium-...

> plihlah Online tools dengan meng click tombol "Help Me Choose" 

Annotation 2022-05-17 154858.png

 

 

 

Semoga ini informasi ini membantu

 

Terima kasih

 

Salam,

Faisal 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-05-17 12:31 AM

1 Like
0
1364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 12:31 AM

Pak @taqin. Tolong dibantu.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
Lieutenant JG

Posted: ‎2022-05-17 12:57 AM

2 Likes
0
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 12:57 AM

Hello 

 

Di schneider panel Primary 24kV mulai dari 25kA, 31,5kA dan 41,5kA

Switchgear 24kV 25kA juga terbagi atas :

1. Gas Insulated Switchgear beberapa product nya adalah GHA, WSB, CBGS dengan rating current mulai dari 630A sampai 4000A

2. Air Insulated Swichgear 24kV 25kA ada beberapa type product MCSET 4 untuk Switchgear dengan CB menggunakan Gas SF6 dan PIX24 untuk pilihan menggunakan CB Vacuum

 

productnya merupakan Engineering To Order (ETO) dibuat berdasarkan kebutuhan dan spesifikasi khusus menyesuaikan kebutuhan 

 

info lebih lanjut bisa di lihat dalam tautan berikut ini 

 

https://www.se.com/ww/en/product-subcategory/87898-primary-air-insulated-switchgear/ 

https://www.se.com/id/en/product-subcategory/87901-primary-gas-insulated-switchgear/

 

silahkan menghubungi sales schneider lebih lanjut untuk product yang diperlukan bila ini adalah sebuah extension atau perlu adanya modifikasi silahkan menghubungi saya dari team service untuk support lebih lanjut 

 

salam 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

faisalamir
Lieutenant faisalamir Lieutenant
Lieutenant

Posted: ‎2022-05-17 01:51 AM

2 Likes
0
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 01:51 AM

Hi Citra,

 

Menambahkan informasi dari rekan-rekan sebelumnya terkait pertimbangan dan pemilihan tipe panel tegangan menengah (panel TM)

 

Maka beberapa informasi dibawah ini perlu diketahui sebagai bagian dari basis data teknis untuk pemilihan tipe panel:

 

 1. Tipe panel TM menggunakan Isolasi Udara (AIS=Air Insulated Swicthgear) atau menggunakan Gas SF6 (GIS=Gas Insulated Switchgear =Fully Insulated Switchgear)?

untuk tipe panel Schneider saat ini baik AIS dan GIS sudah ada opsi dengan menggunakan teknologi yang menggantikan gas SF6 sebagai media breaking capacity dan media Isolasi Dielektrik 

 

2. Info mengenai tegangan, frekuensi, dan kemampuan hantar arus normal terus menerus (KHA)

 

3. Info mengenai tingkat ketahanan arus hubung singkat berikut durasi hubung singkat (dalam detik) 

 

4. Info sistem grounding berikut dengan arus ketahanan gangguan fase-bumi

 

5. Indeks pengaman selangkup dan partisi

 

6. Info mengenai kelas untuk Loss of Service Continuity (LSC1 atau LSC2) dan Partitioning (PM or PI) mengacu pada standard IEC 62271-200

 

Untuk memudahkan pemilihan produk panel TM secara otomatis di web schneider dapat diakses di link berikut:

https://www.se.com/ww/en/product-category/87897-medium-voltage-switchgear/?filter=business-6-medium-...

> plihlah Online tools dengan meng click tombol "Help Me Choose" 

Annotation 2022-05-17 154858.png

 

 

 

Semoga ini informasi ini membantu

 

Terima kasih

 

Salam,

Faisal 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore