Injeksi Primer atau Injeksi Sekunder (Primary & Secondary Injector) pada Circuit Breaker ?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Injeksi Primer atau Injeksi Sekunder (Primary & Secondary Injector) pada Circuit Breaker ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Power Distribution and Digital Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
AntoniusH
Ensign AntoniusH
Ensign

Posted: ‎2022-05-17 05:30 AM . Last Modified: ‎2022-05-17 09:05 AM

1 Like
3
5897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 05:30 AM . Last Modified: ‎2022-05-17 09:05 AM

Injeksi Primer atau Injeksi Sekunder (Primary & Secondary Injector) pada Circuit Breaker ?

Selamat Malam,

 

Mohon dijelaskan apa perbedaan pengetesan dengan Primary Injection dan Secondary Injection ?

 

Kapan kita harus menggunakan Primary dan kapan cukup hanya dengan Secondary Injection seperti pada kebanyakan Circuit breaker ?

Labels
  • Labels:
  • Indonesia
  • Tags:
  • bahasa Indonesia
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
faisalamir
Lieutenant faisalamir Lieutenant
Lieutenant

Posted: ‎2022-05-17 06:07 AM

1 Like
2
5890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 06:07 AM

Hi Pak Antonius,

 

Berikut penjelasan umum mengenai aplikasi primary injection vs secondary injection pada aplikasi pengujian Circuit breaker (CB):

 

Pengujian dengan metode "Secondary injection":

  • Hanya dapat dilakukan untuk CB yang menggunakan modul tipe electronic relay  
  • Dengan secondary injection, persiapan dan eksekusi dalam proses pengujian dapat dilakukan dengan cepat dan hanya menggunakan ukuran cable seusai dengan nilai arus sekunder dengan dilengkapi pengaman lebur 
  • Pengujian dengan secondary injection, obyek pengujian hanya untuk fungsi unit relay/trip unit saja
  • Dimensi dan berat untuk alat secondary injection relatif lebih ringkas dan ringan sehingga mudah untuk mobilisasi
  • Biaya pengujian relative lebih TERJANGKAU

 

Pengujian dengan metode "Primary injection":

  • Dapat dilakukan untuk CB yang menggunakan modul tipe "thermal magnetic" atau "electronic breakers"
  • Dengan primary injection, persiapan dan ekesekusi dalam proses pengujian harus dilakukan dengan persiapan lebih komplek dan mempertimbangkan sisi keamanan dikarenakan melibatkan nilai nominal arus dan tegangan primer. Besaran ukuran kabel dan tambahan pengaman lebur perlu diperhitungkan sesuai dengan nilai nominal arus primer yang akan di injeksi 
  • Dengan primary injection, obyek pengetesan dapat dilakukan secara menyeluruh mulai dari pengetesan akurasi pada CT (trafo arus), pengkabelan dari CT ke modul unit relay, dan pengetesan fungsi unit relay/trip unit itu sendiri
  • Dimensi dan berat untuk alat primary injection relatif lebih besar dan berat sehingga dibutuhkan persiapan yang mobilisasi yang lebih matang
  • Biaya pengujian relatif lebih MAHAL

 

Semoga penjelasan diatas membantu

 

Salam,

Faisal

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
faisalamir
Lieutenant faisalamir Lieutenant
Lieutenant

Posted: ‎2022-05-17 06:07 AM

1 Like
2
5891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 06:07 AM

Hi Pak Antonius,

 

Berikut penjelasan umum mengenai aplikasi primary injection vs secondary injection pada aplikasi pengujian Circuit breaker (CB):

 

Pengujian dengan metode "Secondary injection":

  • Hanya dapat dilakukan untuk CB yang menggunakan modul tipe electronic relay  
  • Dengan secondary injection, persiapan dan eksekusi dalam proses pengujian dapat dilakukan dengan cepat dan hanya menggunakan ukuran cable seusai dengan nilai arus sekunder dengan dilengkapi pengaman lebur 
  • Pengujian dengan secondary injection, obyek pengujian hanya untuk fungsi unit relay/trip unit saja
  • Dimensi dan berat untuk alat secondary injection relatif lebih ringkas dan ringan sehingga mudah untuk mobilisasi
  • Biaya pengujian relative lebih TERJANGKAU

 

Pengujian dengan metode "Primary injection":

  • Dapat dilakukan untuk CB yang menggunakan modul tipe "thermal magnetic" atau "electronic breakers"
  • Dengan primary injection, persiapan dan ekesekusi dalam proses pengujian harus dilakukan dengan persiapan lebih komplek dan mempertimbangkan sisi keamanan dikarenakan melibatkan nilai nominal arus dan tegangan primer. Besaran ukuran kabel dan tambahan pengaman lebur perlu diperhitungkan sesuai dengan nilai nominal arus primer yang akan di injeksi 
  • Dengan primary injection, obyek pengetesan dapat dilakukan secara menyeluruh mulai dari pengetesan akurasi pada CT (trafo arus), pengkabelan dari CT ke modul unit relay, dan pengetesan fungsi unit relay/trip unit itu sendiri
  • Dimensi dan berat untuk alat primary injection relatif lebih besar dan berat sehingga dibutuhkan persiapan yang mobilisasi yang lebih matang
  • Biaya pengujian relatif lebih MAHAL

 

Semoga penjelasan diatas membantu

 

Salam,

Faisal

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-05-17 08:59 AM

In response to faisalamir
1 Like
1
5885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 08:59 AM

Terima kasih Pak Faisal atas penjelasannya.

 

Lengkap dan jelas sekali penjelasannya.

 

Memang dari pengalaman saya 12 tahun di services hanya beberapa pelanggan yang meminta pengujian dengan Primary Injector dikarenakan persiapan yang lebih komplek dan biaya yang pastinya lebih besar dalam eksekusi. Biaya sewa Primary Injector juga jauh lebih mahal daripada secondary. Yang meminta pengujian dengan Primary Injector biasanya customer pengguna daya besar (Power Intensive) yang memiliki dana operasional lebih besar dan yang akan mengalami kerugian besar juga jika ada pemadaman listrik tidak terrencana sehingga mereka mau pengetesan secara menyeluruh seperti penjelasan Pak Faisal.

 

Sebagian besar pelanggan cukup puas dengan Pengujian menggunakan Secondary Injector yang biayanya relatif lebih terjangkau.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-05-17 09:19 AM

In response to HelvinHermanT
0 Likes
0
5878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 09:19 AM

Untuk Circuit Breaker dari Schneider, Electric,  digunakan alat test FFTK (Full Function Test Kit) yang digunakan untuk pengetesan Circuit Breaker pada Micrologicnya (bukan Primary Injector)

 

Testing Micrologic Trip Unit with Full Function Test Kit | Schneider Electric Support 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore