Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Tips pemilihan Busway / Busduct

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Tips pemilihan Busway / Busduct
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
VickyTanzil
Ensign VickyTanzil Ensign
5
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Solved
KKS
Ensign KKS
Ensign

Posted: ‎2022-08-17 10:49 PM

1 Like
3
937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-17 10:49 PM

Tips pemilihan Busway / Busduct

Selamat Pagi,

 

Di market ada banyak yang menawarkan solusi distribusi listrik dengan menggunakan Busway / Busduct / Busbar trunking.

 

Mohon diberikan tips apa saja kriteria pemilihan produk yang baik dan sesuai dengan aplikasinya.

 

Terima kasih/

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Nedi
Nedi Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-08-19 12:38 AM

In response to HelvinHermanT
2 Likes
1
925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-19 12:38 AM

Beberapa hal yang bisa dijadikan acuan pemilihan busduct diantaranya yaitu :

  • Refer ke standard terbaru seperti IEC 61439-6 dengan 25 verifikasi type test
  • Komplit certificate test report termasuk green leaf certificate
  • Walaupun manufacture nya diluar negeri tapi Vendor dan principle pembuat busduct ada di Indonesia
  • Kapasitas rating ampere yang komplit baik LV & MV busduct
  • Konfigurasi Phase + neutral 100% + Earthing komplit sesuai kebutuhan proyek
  • Bisa digunakan untuk aplikasi indoor & outdoor sesuai IP rating
  • Kemurnian kandungan material konduktor CU maupun AL diatas 98% dan ditunjukan dengan test report nya
  • Project reference yang banyak dan komplit diberbagai bidang sektor industri

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-08-18 02:33 AM

0 Likes
2
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-18 02:33 AM

@Nedi 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Nedi
Nedi Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-08-19 12:38 AM

In response to HelvinHermanT
2 Likes
1
926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-19 12:38 AM

Beberapa hal yang bisa dijadikan acuan pemilihan busduct diantaranya yaitu :

  • Refer ke standard terbaru seperti IEC 61439-6 dengan 25 verifikasi type test
  • Komplit certificate test report termasuk green leaf certificate
  • Walaupun manufacture nya diluar negeri tapi Vendor dan principle pembuat busduct ada di Indonesia
  • Kapasitas rating ampere yang komplit baik LV & MV busduct
  • Konfigurasi Phase + neutral 100% + Earthing komplit sesuai kebutuhan proyek
  • Bisa digunakan untuk aplikasi indoor & outdoor sesuai IP rating
  • Kemurnian kandungan material konduktor CU maupun AL diatas 98% dan ditunjukan dengan test report nya
  • Project reference yang banyak dan komplit diberbagai bidang sektor industri
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-08-19 01:08 AM

In response to Nedi
1 Like
0
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-19 01:08 AM

Terima kasih Pak Nedi,

 

Mungkin satu lagi yang tidak kalah penting :

 

Pastikan produk memiliki dukungan layanan purna jual yang lengkap dan handal.

Baik dalam penyediaan suku cadang, layanan troubleshooting, layanan perbaikan, layanan perawatan / maintenance, dll.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore