Posted: 2021-11-08 11:45 PM
Untuk Energy Effisiensi Listrik, Bapak bisa melihat IEC 60364-8-1 atau PUIL 2020 bagian 8-1 Aspek fungsional – Efisiensi Energi
Standar ini memperkenalkan persyaratan, rekomendasi dan metode untuk desain dan asesmen efisiensi energi instalasi listrik dalam kerangka pendekatan manajemen efisiensi energi untuk mendapatkan layanan yang setara secara fungsional permanen terbaik untuk konsumsi energi listrik terendah dan ketersediaan energi dan keseimbangan ekonomi yang paling dapat diterima.
Bagian PUIL ini memberikan persyaratan, tindakan dan rekomendasi tambahan untuk desain, pemasangan, operasi dan verifikasi semua jenis instalasi listrik voltase rendah, termasuk produksi lokal dan penyimpanan energi untuk mengoptimalkan semua penggunaan tenaga listrik yang efisien.
Dokumen ini mengenalkan persyaratan, rekomendasi dan metode untuk desain dan asesmen efisiensi energi instalasi listrik dalam kerangka pendekatan manajemen efisiensi energi untuk mendapatkan layanan yang ekuivalen secara fungsional permanen terbaik untuk konsumsi energi listrik yang terendah dan ketersediaan energi dan keseimbangan ekonomi yang paling dapat diterima.
Persyaratan, rekomendasi dan metode ini berlaku, dalam ruang lingkup PUIL (semua bagian), untuk instalasi baru dan modifikasi instalasi yang sudah ada.
Dokumen ini dapat diterapkan pada instalasi listrik gedung atau sistem dan tidak berlaku untuk produk. Efisiensi energi produk dan persyaratan operasionalnya tercakup dalam standar produk yang relevan.
Bila standar lain memberikan persyaratan spesifik untuk penerapan sistem atau instalasi khusus (misalnya sistem manufaktur yang tercakup dalam ISO 20140 (semua bagian)), persyaratan tersebut dapat menggantikan dokumen ini.
Untuk lebih jelasnya silahkan dilihat dalam Standar tersebut.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-07 07:58 PM . Last Modified: 2021-11-07 08:02 PM
Pak Yorga @sesa190510_brid
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-08 11:45 PM
Untuk Energy Effisiensi Listrik, Bapak bisa melihat IEC 60364-8-1 atau PUIL 2020 bagian 8-1 Aspek fungsional – Efisiensi Energi
Standar ini memperkenalkan persyaratan, rekomendasi dan metode untuk desain dan asesmen efisiensi energi instalasi listrik dalam kerangka pendekatan manajemen efisiensi energi untuk mendapatkan layanan yang setara secara fungsional permanen terbaik untuk konsumsi energi listrik terendah dan ketersediaan energi dan keseimbangan ekonomi yang paling dapat diterima.
Bagian PUIL ini memberikan persyaratan, tindakan dan rekomendasi tambahan untuk desain, pemasangan, operasi dan verifikasi semua jenis instalasi listrik voltase rendah, termasuk produksi lokal dan penyimpanan energi untuk mengoptimalkan semua penggunaan tenaga listrik yang efisien.
Dokumen ini mengenalkan persyaratan, rekomendasi dan metode untuk desain dan asesmen efisiensi energi instalasi listrik dalam kerangka pendekatan manajemen efisiensi energi untuk mendapatkan layanan yang ekuivalen secara fungsional permanen terbaik untuk konsumsi energi listrik yang terendah dan ketersediaan energi dan keseimbangan ekonomi yang paling dapat diterima.
Persyaratan, rekomendasi dan metode ini berlaku, dalam ruang lingkup PUIL (semua bagian), untuk instalasi baru dan modifikasi instalasi yang sudah ada.
Dokumen ini dapat diterapkan pada instalasi listrik gedung atau sistem dan tidak berlaku untuk produk. Efisiensi energi produk dan persyaratan operasionalnya tercakup dalam standar produk yang relevan.
Bila standar lain memberikan persyaratan spesifik untuk penerapan sistem atau instalasi khusus (misalnya sistem manufaktur yang tercakup dalam ISO 20140 (semua bagian)), persyaratan tersebut dapat menggantikan dokumen ini.
Untuk lebih jelasnya silahkan dilihat dalam Standar tersebut.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-10 01:34 AM
Apakah standar tersebut ditujukan untuk semua aplikasi Pak @HelvinHermanT ?
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-10 09:17 PM
Hi Pak,
Standar tersebut mengacu kepada bagunan tempat tinggal (Residential building), gedung komersial dan gedung industri (industrial building). Standar tidak meregulasi effisiensi energi pada Transmisi Listrik dan Pembangkit.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-15 05:44 AM
Pendekatan Effisiensi Energi pada intalasi listrik mengacu pada 3 pendekatan :
1. Minimalisasi rugi rugi energi listrik : Optimalisasi rugi ruhi pada perkawatan listrik
2. Penggunaan energi yang tepat, pada saat diperlukan dan dengan biaya rendah : Optimalisasi penggunaan listrik dengan pengendalian instalasi listrik (Energy Efficiency Management System)
3. Mempertahankan performa : Metoda Siklus Hidup (Life Cycle) dan Metode untuk mengases (assestment)
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-17 07:15 PM . Last Modified: 2021-11-17 07:16 PM
Untuk metode assessment nya bagaimana ya Pak @HelvinHermanT ?
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-18 08:41 PM
Hi Pak,
Untuk Metode assestment bisa dilihat pada Annex B (Method to asses the energy efficiency of an electrical installation.
Contoh untuk Industrial, Commercial Building dan Infrastruktur metode assesmen berdasarkan tabel ini :
Detailnya Silahkan dilihat dalam standar tersebut
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-19 05:04 PM
Manfaat apa ya Pak @HelvinHermanT dari penerapan standar ini?
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-21 07:17 PM
Manfaat utama untuk menerapkan standar ini:
DASAR-DASAR untuk pendekatan EE Energi Effisiensi
- Semua praktik EE Terbaik untuk Distribusi Listrik
- Metodologi asestment / penilaian untuk efisiensi energi pada instalasi listrik.
Standar ini mencakup :
- Pengurangan kerugian daya secara permanen
- Penggunaan energi listrik yang lebih baik selama operasi
Konsekuensinya :
- Berkurangnya tagihan listrik
Keuntungan Utama:
- Green Building / Bangunan Hijau (yaitu semua proyek Bangunan):
IEC 60364-8-1 menyediakan kontribusi yang relevan & kunci untuk BIM/BEM/SIM untuk distribusi listrik pada semua fase siklus hidup.
Manfaat lain :
- Ketersediaan tinggi (High availability)
- Penghematan biaya
- Profitabilitas
Keamanan di wilayah hukum melalui standar internasional
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-21 07:22 PM . Last Modified: 2021-11-21 07:26 PM
Untuk referensi Energy Effisiensi dari Schneider Electric, bisa dilihat dalam link dibawah ini
https://www.se.com/id/en/work/services/energy-and-sustainability/energy-efficiency-projects/
Energy Efficiency Consulting
Remote Energy Monitoring
Building a Case for Efficiency - eBook : 4 key steps to build an internal business case to fund energy efficiency programs
https://perspectives.se.com/latest-perspectives/building-a-case-for-efficiency-ebook
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-21 07:46 PM
Baik, terima kasih banyak atas informasinya lengkapnya Pak @HelvinHermanT !
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.