Posted: 2021-07-12 06:33 AM
Kapasitas MCCB/ACB dalam suatu panel induk (incoming) sebenarnya berapa persen dari kapasitas MCCB/ACB tsb?
Malam, mau tanya, kapasitas MCCB/ACB dalam suatu panel induk (incoming) kekuatan sebenarnya berapa persen dari kapasitas MCCB/ACB tsb? Thanks.
- Labels:
-
Indonesia
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-13 09:08 PM
Hi Pak,
Menurut UL489, circuit breaker standar 80% rated. Artinya dalam disain untuk continous maupun uncontinous load, bisa menggunakan 80% rated load dari sebuah circuit breaker.
Jika membutuhkan 100% rated load dari circuit breaker, maka memerlukan paduan Circuit Breaker dan Enclosure (Panel Box) yang didisain baik sehingga bisa 100% rated load (tanpa menyebabkan panas berlebih).
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-13 09:08 PM
Hi Pak,
Menurut UL489, circuit breaker standar 80% rated. Artinya dalam disain untuk continous maupun uncontinous load, bisa menggunakan 80% rated load dari sebuah circuit breaker.
Jika membutuhkan 100% rated load dari circuit breaker, maka memerlukan paduan Circuit Breaker dan Enclosure (Panel Box) yang didisain baik sehingga bisa 100% rated load (tanpa menyebabkan panas berlebih).
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-14 02:35 AM
Terima kasih Pak @HelvinHermanT infonya.
Untuk 100% rated MCCB/ACB. apakah Schneider punya Pak?