Kapasitas MCCB/ACB dalam suatu panel induk (incoming) sebenarnya berapa persen dari kapasitas MCCB/ACB tsb?

Expert on Demand for Standards & Regulations

Solved
RahmatMandala
Crewman
Crewman
0 Likes
2
198

Kapasitas MCCB/ACB dalam suatu panel induk (incoming) sebenarnya berapa persen dari kapasitas MCCB/ACB tsb?

Malam, mau tanya, kapasitas MCCB/ACB dalam suatu panel induk (incoming) kekuatan sebenarnya berapa persen dari kapasitas MCCB/ACB tsb? Thanks.


Accepted Solutions
HelvinHermanT
Captain Captain
Captain
0 Likes
1
192

Re: Kapasitas MCCB/ACB dalam suatu panel induk (incoming) sebenarnya berapa persen dari kapasitas MCCB/ACB tsb?

Hi Pak,

 

Menurut UL489, circuit breaker standar 80% rated. Artinya dalam disain untuk continous maupun uncontinous load, bisa menggunakan 80% rated load dari sebuah circuit breaker.

Jika membutuhkan 100% rated load dari circuit breaker, maka memerlukan paduan Circuit Breaker dan Enclosure (Panel Box) yang didisain baik sehingga bisa 100% rated load (tanpa menyebabkan panas berlebih).

 

@HendySE @JuneventV 

See Answer In Context

Tags (1)
2 Replies 2
HelvinHermanT
Captain Captain
Captain
0 Likes
1
193

Re: Kapasitas MCCB/ACB dalam suatu panel induk (incoming) sebenarnya berapa persen dari kapasitas MCCB/ACB tsb?

Hi Pak,

 

Menurut UL489, circuit breaker standar 80% rated. Artinya dalam disain untuk continous maupun uncontinous load, bisa menggunakan 80% rated load dari sebuah circuit breaker.

Jika membutuhkan 100% rated load dari circuit breaker, maka memerlukan paduan Circuit Breaker dan Enclosure (Panel Box) yang didisain baik sehingga bisa 100% rated load (tanpa menyebabkan panas berlebih).

 

@HendySE @JuneventV 

Tags (1)
RahmatMandala
Crewman
Crewman
0 Likes
0
189

Re: Kapasitas MCCB/ACB dalam suatu panel induk (incoming) sebenarnya berapa persen dari kapasitas MCCB/ACB tsb?

Terima kasih Pak @HelvinHermanT infonya.
Untuk 100% rated MCCB/ACB. apakah Schneider punya Pak?

Tags (1)