Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

IEC 61436 LV panel, to consider NF C 15-100?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • IEC 61436 LV panel, to consider NF C 15-100?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
HelvinHermanT Leader
106
faisalamir
faisalamir Mentor
7
Dwinanto_Setyadi
Dwinanto_Setyadi Troubleshooter
7
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Power Distribution and Digital Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Expert on Demand for Standards & Regulations
Start a Topic
Paul_Loke
Paul_Loke Explorer
Explorer

Posted: ‎2021-04-07 08:58 AM

0 Likes
2
4053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-07 08:58 AM

IEC 61436 LV panel, to consider NF C 15-100?

Hi,

 

I hope someone can help me on this.

 

Question with regards to participation in the ITER project.

When assembling IEC 61436 LV panel, do we have to consider NFC 15-100? What are the differences between NFC 15-100 and IEC 60364 when applying to IEC 61439 panels?

 

Thank you. 

 

PL

 

@Philippe_Vollet

Labels
  • Labels:
  • Singapore
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Philippe_Vollet
Philippe_Vollet Leader
Leader

Posted: ‎2021-04-07 09:55 AM . Last Modified: ‎2021-04-08 12:11 AM

0 Likes
1
4047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-07 09:55 AM . Last Modified: ‎2021-04-08 12:11 AM

Dear Paul, 

The IEC 61439 Serie "Low-voltage switchgear and controlgear assemblies" have been developed in order to provide to the End-Users of switchboards a high level of confidence in terms of safety and power availability.

The IEC 60364 Serie is the international standard for the "Low Voltage Electrical Installations", and serve as a basis for national standardization, as for example NFC15100 for France

 

IEC 61439 requirements are intended to ensure that the required protective measures are obtained when an assembly is installed in an electrical system conforming to the IEC 60364 series.

 

Please find several documents for more information:

https://blog.se.com/power-management-metering-monitoring-power-quality/2018/05/10/avoid-the-wrong-ty...

https://www.electrical-installation.org/enwiki/The_installation_system

https://www.electrical-installation.org/enwiki/Main_Page

 

 @PascalL : Any additional comments ?

BR

Philippe

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

PascalL
PascalL Leader
Leader

Posted: ‎2021-04-08 12:43 AM

In response to Philippe_Vollet
0 Likes
0
4030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-08 12:43 AM

Dear all,

 

Usually when I explain the position and the use of the IEC standards I say,

 

First, we use product according to their product standard as IEC60947 series and for example IEC60947-2 for breakers

 

Second, we use assembly standard as 61439 series and for example IEC61439-2 to PSC assemblies or IEC61439-6 to (BTS) busbar trunking system

 

third, finally we use installation rules standards as IEC60364series and for Fr the local standard is NF C 15-100.

 

Best regards,

PascalL

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore