Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Bagaimana Ketentuan Penggunaan ELCB di rumah tinggal ?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Bagaimana Ketentuan Penggunaan ELCB di rumah tinggal ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Power Distribution and Digital Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Expert on Demand for Standards & Regulations
Start a Topic
CitraR
Ensign CitraR
Ensign

Posted: ‎2023-05-24 08:59 PM

0 Likes
3
3683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-24 08:59 PM

Bagaimana Ketentuan Penggunaan ELCB di rumah tinggal ?

Selamat Siang,

 

Saya melihat beberapa perumahan baru sudah dilengkapi dengan tambahan ELCB selain menggunakan MCB.

 

Yang saya ketahui bahwa ELCB digunakan untuk perlindungan bahaya kesetrum dan kebakaran.

 

Pertanyaan saya bagaimana sih ketentuan penggunaan ELCB untuk rumah tinggal ?

Apakah ELCB hanya digunakan untuk Proteksi bahaya kesetrum pada Pemanas Air atau bagaimana ?

 

Terima kasih.

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2023-05-25 06:36 AM

0 Likes
2
3672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-25 06:36 AM

Selamat Malam,

 

ELCB atau RCCB adalah alat proteksi arus sisa atau disebut GPAS (Gawai Proteksi Arus sisa) dalam Standar PUIL 2020. Pada Standar IEC disebut sebagai RCD (Residual Current Device).

 

GPAS adalah alat yang digunakan untuk memproteksi bahaya kesetrum akibat arus yang bocor dalam sistem kelistrikan. Biasanya diakibatkan kondisi pelindung /insulator kabel yang sudah tidak baik sehingga mengakibatkan kebocoran arus yang mengakibatkan kejut listrik / kesetrum.

 

GPAS yang diperuntukan bagi aplikasi rumah dibagi menjadi 2 kategori sensitivitas yaitu

1. GPAS 30mA memiliki sensitivitas 30mA untuk melindungi bahaya kesetrum

2. GPAS 300mA memiliki sensitivitas 300mA untuk melindungi bahaya kebakaran akibat arus sisa.

 

GPAS 30mA banyak digunakan untuk proteksi kesetrum pada rumah tinggal.

Gambar dibawah memperlihatkan pengarus arus terhadap tubuh manusia.

HelvinHermanT_0-1685021590495.png

Berikut gambar GPAS/RCCB/ELCB :

 

HelvinHermanT_2-1685021767247.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2023-05-25 06:48 AM

In response to HelvinHermanT
0 Likes
1
3671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-25 06:48 AM

Untuk Pertanyaan mengenai ketentuan pemakaian GPAS/RCCB/ELCB dirumah, maka kita harus mengacu kepada standar instalasi listrik yaitu PUIL 2020 (Persyaratan Umum Instalasi Listrik) yang mana keluaran terakhir pada Tahun 2020 dengan nomer SNI 0225.

 

Pada "PUIL 2020 – Bagian 4-41: Proteksi untuk keselamatan – Proteksi terhadap kejut" pada pasal 411.3.3 menyebutkan bahwa :

 

"Proteksi tambahan dengan GPAS dengan operasi arus sisa tidak lebih dari 30mA harus disediakan untuk :

- Stopkontak a.b dengan arus pengenal tidak melebihi 32A yang akan digunakan oleh orang awam dan dimaksudkan untuk penggunaan umum.

 

Dari ketentuan PUIL 2020 diatas maka stopkontak rumah dipersyaratkan untuk menggunakan GPAS/RCCB/ELCB karena memiliki arus <32A dan digunakan oleh orang awam untuk berbagai keperluan.  

Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2023-05-25 07:01 AM . Last Modified: ‎2023-05-25 07:02 AM

In response to HelvinHermanT
0 Likes
0
3671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-25 07:01 AM . Last Modified: ‎2023-05-25 07:02 AM

Mengenai ELCB/GPAS/RCCB yang digunakan oleh Pemanas Air, hal ini sudah sesuai dengan Persyaratan PUIL 2020 seperti yang diatur pada "PUIL 2020 – Bagian 7-701: Persyaratan untuk instalasi atau lokasi khusus – Lokasi berisi bak atau dus". 

 

Pada PUIL 2020 – Bagian 7-701 pasal 415.1 menyebutkan :

Dalam ruang yang berisikan bak atau dus (shower), satu atau lebih GPAS dengan arus operasi sisa tidak melebihi 30mA harus memberikan proteksi pada semua sirkit.

 

HelvinHermanT_5-1685022890043.png

 

Oleh karena itu maka semua sirkit pada lokasi bak mandi / shower harus diproteksi dengan GPAS 30mA untuk proteksi bahaya kesetrum.

 

Selain PUIL diatas, juga ada beberapa ketentuan untuk lokasi sejenis yaitu :

1. PUIL 2020 - Bagian 7-702: Persyaratan untuk instalasi atau lokasi khusus – Kolam renang dan air mancur

2. PUIL 2020 - Bagian 7-703: Persyaratan untuk instalasi atau lokasi khusus – Ruangan dan kabin berisi pemanas sauna

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore