Apa saja standar design instalasi untuk rumah sakit ya?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Apa saja standar design instalasi untuk rumah sakit ya?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 02:52 AM

1 Like
5
3160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 02:52 AM

Apa saja standar design instalasi untuk rumah sakit ya?

Sore, Apa saja standar design instalasi untuk rumah sakit ya? Thanks

Labels
  • Labels:
  • Indonesia
  • Tags:
  • bahasa Indonesia
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-07-11 08:39 PM . Last Modified: ‎2021-07-11 09:28 PM

1 Like
0
3150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 08:39 PM . Last Modified: ‎2021-07-11 09:28 PM

Terima kasih atas pertanyaannya.

 

Berikut standar instalasi untuk rumah sakit :

 

IEC 60364-7-710:2021 Low-voltage electrical installations - Part 7-710: Requirements for special installations or locations - Medical locations


SNI 0225-7-710:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-710: Persyaratan untuk instalasi atau lokasi khusus – Lokasi medis.

 

@FerryKurniawan 

See Answer In Context

  • Tags:
  • bahasa Indonesia
Reply

Link copied. Please paste this link to share this article on your social media post.

FerryKurniawan
Ensign FerryKurniawan Ensign
Ensign

Posted: ‎2021-07-11 09:18 PM

1 Like
3
3140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 09:18 PM

Hi Pak Estiono,

 

Saat ini standar desain instalasi untuk RS yang berhubungan dengan solusi dari Schneider adalah Permenkes No. 2306 Tahun 2011 untuk Instalasi Elektrikal RS (diadaptasi dari standar IEC) dan Pedoman Teknis Sistem Instalasi Tata Udara Kementerian Kesehatan Tahun 2012 (diadaptasi dari standar ASHRAE).Terdapat juga Permenkes No. 24 Tahun 2016 tentang Persyaratan Teknis Bangunan & Prasarana Rumah Sakit yang mengatur bagaimana masing-masing area di dalam fasilitas RS perlu dirancang guna mendukung keselamatan pasien dan tenaga medis.

 

Solusi dari Schneider yang dapat membantu RS untuk memenuhi standar-standar diatas diantaranya adalah Panel Kubikel Tegangan Menengah, komponen Panel Tegangan Rendah dan Distribusi Akhir, UPS, Panel Isolasi dan sistem BMS untuk mengontrol dan memanage tata udara di area RS.

 

Semoga penjelasan ini membantu, jika ada yang kurang jelas silahkan direply dan ditanyakan kembali ke kami Pak, terima kasih.

See Answer In Context

  • Tags:
  • design
  • english
  • healthcare
  • hospital
  • regulasi
  • rumahsakit
  • standar
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-07-11 08:39 PM . Last Modified: ‎2021-07-11 09:28 PM

1 Like
0
3151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 08:39 PM . Last Modified: ‎2021-07-11 09:28 PM

Terima kasih atas pertanyaannya.

 

Berikut standar instalasi untuk rumah sakit :

 

IEC 60364-7-710:2021 Low-voltage electrical installations - Part 7-710: Requirements for special installations or locations - Medical locations


SNI 0225-7-710:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-710: Persyaratan untuk instalasi atau lokasi khusus – Lokasi medis.

 

@FerryKurniawan 

  • Tags:
  • bahasa Indonesia
Reply

Link copied. Please paste this link to share this article on your social media post.

FerryKurniawan
Ensign FerryKurniawan Ensign
Ensign

Posted: ‎2021-07-11 09:18 PM

1 Like
3
3141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 09:18 PM

Hi Pak Estiono,

 

Saat ini standar desain instalasi untuk RS yang berhubungan dengan solusi dari Schneider adalah Permenkes No. 2306 Tahun 2011 untuk Instalasi Elektrikal RS (diadaptasi dari standar IEC) dan Pedoman Teknis Sistem Instalasi Tata Udara Kementerian Kesehatan Tahun 2012 (diadaptasi dari standar ASHRAE).Terdapat juga Permenkes No. 24 Tahun 2016 tentang Persyaratan Teknis Bangunan & Prasarana Rumah Sakit yang mengatur bagaimana masing-masing area di dalam fasilitas RS perlu dirancang guna mendukung keselamatan pasien dan tenaga medis.

 

Solusi dari Schneider yang dapat membantu RS untuk memenuhi standar-standar diatas diantaranya adalah Panel Kubikel Tegangan Menengah, komponen Panel Tegangan Rendah dan Distribusi Akhir, UPS, Panel Isolasi dan sistem BMS untuk mengontrol dan memanage tata udara di area RS.

 

Semoga penjelasan ini membantu, jika ada yang kurang jelas silahkan direply dan ditanyakan kembali ke kami Pak, terima kasih.

  • Tags:
  • design
  • english
  • healthcare
  • hospital
  • regulasi
  • rumahsakit
  • standar
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-12 06:03 AM

In response to FerryKurniawan
0 Likes
2
3131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 06:03 AM

Terima kasih infonya @Pak @HelvinHermanT dan Pak @FerryKurniawan .

SNI 0225-7-710:2020 berarti adaptasi dari IEC 60364-7-710:2021 ya Pak, karena saya lihat judulnya sama.
Untuk Permenkes No. 2306 Tahun 2011 apakah adaptasi dari IEC 60364-7-710:2021 juga?

Terima kasih!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-07-15 11:34 PM . Last Modified: ‎2021-07-15 11:35 PM

In response to Anonymous user
0 Likes
1
3119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-15 11:34 PM . Last Modified: ‎2021-07-15 11:35 PM

Hi Pak,

 

Benar Pak.

 

Sebagai contoh untuk standard Instalasi Kelisrikan, Badan Standarisasi Indonesia membuat suatu Standar Nasional (SNI) yang di susun oleh Komite Teknis di Indonesia.

 

Standar Internasional untuk Instalasi Listrik disusun oleh Komite Teknis IEC dilevel Global yang beriisikan perwakilan Tenaga Ahli dari setiap negara yang menjadi anggota IEC. Indonesia juga memiliki perwakilan dalam team Komite Teknis IEC Global (saya salah satunya). Hasil dari IEC Global adalah suatu Standar IEC (contoh : IEC 60364-7-710:2021)

 

Indonesia sendiri memiliki Team Komite Nasional Lokal (atau disebut IEC Mirror Commitee) yang berisikan para Tenaga Ahli di Indonesia. Tugas team tersebut adalah mendiskusikan, merumuskan dan menyusun Standar Nasional (SNI). Hasil dari team Komite Nasional Indonesia adalah suatu standard SNI (Contoh : SNI 0225-7-710:2020).

 

Standard yang diterapkan di Indonesia tentunya mengacu juga ke standar Internasional yang diadopsi secara utuh atau dimodifikasi sesuai kebijakan Lokal. Semua ini untuk melindungi kepentingan Masyarakat Indonesia dan sekaligus menjamin diterimanya suatu produk oleh dunia internasional.

  • Tags:
  • bahasa Indonesia
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-10-05 09:37 PM

In response to HelvinHermanT
0 Likes
0
3010
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-05 09:37 PM

Oke Pak, terima kasih Pak atas penjelasannya

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore