Problem med att byta modul/givartyp på luftbehandlingsaggregat

EcoStruxure SEAL Forum

This forum is for engineers working EcoStruxure Building Operation, wanting to leverage the SEAL application to improve the efficiency in the engineering process.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • EcoStruxure SEAL Forum
  • Problem med att byta modul/givartyp på luftbehandlingsaggregat
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
StefanLundin
Commander StefanLundin Commander
30
Benji
Administrator Benji Administrator
9
Jim.T
Ensign Jim.T Ensign
4
APA
Lieutenant APA Lieutenant
3
View All
Related Products
product field
Schneider Electric
EcoStruxure SEAL

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure SEAL Forum
Solved
flippipippi
flippipippi
Cadet

Posted: ‎2025-06-18 05:23 AM

0 Likes
4
44
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-18 05:23 AM

Problem med att byta modul/givartyp på luftbehandlingsaggregat

håller på att skapa lite I/O listor medhjälp av SEAL och alla givare verkar lägga sig på en UI-16 när jag vill ha dem på en RTD-16 för PT1000 support.

 

Det verkar inte gå att ändra givartypen för då kraschar SEAL

kan inte heller binda om alla givare till en ny RTD-16 modul i SEAL, då kraschar SEAL

Finns det nån lösning? gör jag nått fel?

Labels
  • Labels:
  • Swedish
  • Tags:
  • english
  • Swedish
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
StefanLundin
Commander StefanLundin Commander
Commander

Posted: ‎2025-06-19 02:31 AM . Last Modified: ‎2025-06-19 02:34 AM

0 Likes
0
21
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-19 02:31 AM . Last Modified: ‎2025-06-19 02:34 AM

@flippipippi  Tack för filen , jag kunde med hjälp av den återskapa ditt problem med frånluftsfläktsapplikationen, det finns nu ett uppdaterat bibliotek utlagt som åtgärdar problemet, så om du nu öppnar upp din solution igen nu så borde du kunna ändra dina givare till PT1000.  

Jag kunde också se ett problem som kan uppstå  vid användningen av PT1000 - 3 Wire som kanske skapade problemet för dig för Luftbehandlingsaggregatet i början.  När man använder 3-wire konfigurationer på en RTD-DI-16 Modul så tar dessa konfigurationer i verkligheten upp två IO punkter ( den man konfigurerar den mot + efterföljande) , detta är inget vi idag i SEAL hindrar användaren att från att försöka göra.

Så om du behöver använda en 3-wire konfiguration av en Pt1000/Pt100/Ni1000/LG-Ni1000 så måste man själv se till att efterföljande IO inte används, annars får man ett felmeddelande vid nedladdningen som inte är så tydligt. 

Error: Error when saving data to server! 
    Method SyncInvokeSave failed. [Code=InvalidData, DisplayInfo='IDSortManager::Sort - ID 2 referenced 2 times', TechnicalInfo='',
Module=AutomationServerIoBus, ModuleCode=1]


Jag har noterat att detta meddelande behöver få ett mycket tydligare meddelande.  

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
flippipippi
flippipippi
Cadet

Posted: ‎2025-06-18 10:37 PM

0 Likes
0
20
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-18 10:37 PM

det verkar hjälpa att Unassign dessa givarobjekt innan man ändrar givartyp. smh

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

StefanLundin
Commander StefanLundin Commander
Commander

Posted: ‎2025-06-18 10:53 PM . Last Modified: ‎2025-06-18 10:54 PM

0 Likes
0
41
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-18 10:53 PM . Last Modified: ‎2025-06-18 10:54 PM

Hej @flippipippi  , Jag testade lite snabbt på min sida utan att få problem, kan du skicka mig din soultion fil så får vi titta närmre på ditt specifika projekt. Antingen via att ladda upp den här, eller via ett privat meddelande till mig. 

Kan du även komplettera med information om vilken version av SEAL du använder , vilken EBO Server version det tänkt att du skall använda den till, och vilken version av Luftbehandlings biblioteket du använder (Hoovra  över rubriken )

StefanLundin_0-1750312356935.png

 



Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

flippipippi
flippipippi
Cadet

Posted: ‎2025-06-18 11:12 PM

0 Likes
0
33
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-18 11:12 PM

SEAL (1.15.1.0)

Luftbehandlingsaggregat (4.0.4)

EBO??? jag är väldigt ny till schneider så det steget har jag ej kommit till än, (din rekomendation?)

 

jag lyckades binda om och lyckades ändra typ på några (Man måste unbind innan man kan ändra typ...)

har dock problem med att ändra givartyp på FF09-GT31 Till 2-wire PT1000. då kraschar det.

 

 

 

 

Attachments
AS05.rar
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

StefanLundin
Commander StefanLundin Commander
Commander

Posted: ‎2025-06-19 02:31 AM . Last Modified: ‎2025-06-19 02:34 AM

0 Likes
0
22
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-19 02:31 AM . Last Modified: ‎2025-06-19 02:34 AM

@flippipippi  Tack för filen , jag kunde med hjälp av den återskapa ditt problem med frånluftsfläktsapplikationen, det finns nu ett uppdaterat bibliotek utlagt som åtgärdar problemet, så om du nu öppnar upp din solution igen nu så borde du kunna ändra dina givare till PT1000.  

Jag kunde också se ett problem som kan uppstå  vid användningen av PT1000 - 3 Wire som kanske skapade problemet för dig för Luftbehandlingsaggregatet i början.  När man använder 3-wire konfigurationer på en RTD-DI-16 Modul så tar dessa konfigurationer i verkligheten upp två IO punkter ( den man konfigurerar den mot + efterföljande) , detta är inget vi idag i SEAL hindrar användaren att från att försöka göra.

Så om du behöver använda en 3-wire konfiguration av en Pt1000/Pt100/Ni1000/LG-Ni1000 så måste man själv se till att efterföljande IO inte används, annars får man ett felmeddelande vid nedladdningen som inte är så tydligt. 

Error: Error when saving data to server! 
    Method SyncInvokeSave failed. [Code=InvalidData, DisplayInfo='IDSortManager::Sort - ID 2 referenced 2 times', TechnicalInfo='',
Module=AutomationServerIoBus, ModuleCode=1]


Jag har noterat att detta meddelande behöver få ett mycket tydligare meddelande.  

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of