Posted: 2025-02-12 03:14 AM
Hi Seal community,
Today i'm trying to use seal script with an ASP on PCT2 and i have an access error. After many tests i found that i can access with ASP version 4, version 6, version 3 on PCT 2.0 but not V5 (all ASP on V5 is failed).
Has someone have an idea to fix it?
Access by workstation is OK.
same by seal :
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-12 03:24 AM
Hi Mikael,
By the message you get, it looks like you perhaps are missing a hotfix for your workstation.
The Release notes for PCT 2 tells you that you must install EBO workstation hotfix 5.0.3.5001-CP4 or later to work with PCT2. The corresponding Hotfix needs to be installed if you are using older versions of EBO Workstation as well.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-12 03:24 AM
Hi Mikael,
By the message you get, it looks like you perhaps are missing a hotfix for your workstation.
The Release notes for PCT 2 tells you that you must install EBO workstation hotfix 5.0.3.5001-CP4 or later to work with PCT2. The corresponding Hotfix needs to be installed if you are using older versions of EBO Workstation as well.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-12 04:22 AM . Last Modified: 2025-02-12 04:22 AM
New tests, i upgraded V5.0.3 to 6.0.3, now i can access to this ASP !!!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-12 11:24 PM
Hi Stefan, you're right my workstation is not at the good version, hotfix fixes it. I'm surprise because in my mind i've done for V6 and V5 in the same time. Maybe i need to seal script my brain. Thanks a lot.