Connecting to PCT server issue

EcoStruxure SEAL Forum

This forum is for engineers working EcoStruxure Building Operation, wanting to leverage the SEAL application to improve the efficiency in the engineering process.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • EcoStruxure SEAL Forum
  • Connecting to PCT server issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
StefanLundin
Lt. Commander StefanLundin Lt. Commander
25
Benji
Administrator Benji Administrator
9
MortenEnger
Lieutenant JG MortenEnger Lieutenant JG
3
APA
Lieutenant JG APA Lieutenant JG
3
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure SEAL Forum
Solved
Jagadeesh_01
Lieutenant JG Jagadeesh_01
Lieutenant JG

Posted: ‎2025-04-15 07:30 PM

0 Likes
3
259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-15 07:30 PM

Connecting to PCT server issue

Hi all,

I'm trying to connect to PCT ASP/ES and I'm getting some error. I tried both secure and non-secure communication, both not working. Attached both error screens. How do we connect SEAL tool to PCT server. Has anyone faced the similar issue? We are using the Latest Ubuntu PCT Beta version.

 

Thanks,

Jagadeesh S 

Error 2 http.jpg

Error 1 https.jpg

Labels
  • Labels:
  • Connectivity
  • PCT
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
StefanLundin
Lt. Commander StefanLundin Lt. Commander
Lt. Commander

Posted: ‎2025-04-15 10:20 PM . Last Modified: ‎2025-04-15 10:28 PM

2 Likes
0
239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-15 10:20 PM . Last Modified: ‎2025-04-15 10:28 PM

Hello Jagadeesh
What EBO Version are you trying to connect to ? 
The message you get looks like similar to the one you get when you haven't installed the correct hotfix for your workstation. So if the PCT server is less than EBO 6, ensure you have the latest hotfix installed. 
The Release notes for PCT 2 tells you that you must install EBO workstation hotfix 5.0.3.5001-CP4 or later to work with PCT2. The corresponding Hotfix needs to be installed if you are using older versions of EBO Workstation as well. 
 
(and also, not related to this but please update to SEAL 1.14.2 since 1.14.1 had some issues that has been fixed in 1.14.2 )

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
StefanLundin
Lt. Commander StefanLundin Lt. Commander
Lt. Commander

Posted: ‎2025-04-15 10:20 PM . Last Modified: ‎2025-04-15 10:28 PM

2 Likes
0
240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-15 10:20 PM . Last Modified: ‎2025-04-15 10:28 PM

Hello Jagadeesh
What EBO Version are you trying to connect to ? 
The message you get looks like similar to the one you get when you haven't installed the correct hotfix for your workstation. So if the PCT server is less than EBO 6, ensure you have the latest hotfix installed. 
The Release notes for PCT 2 tells you that you must install EBO workstation hotfix 5.0.3.5001-CP4 or later to work with PCT2. The corresponding Hotfix needs to be installed if you are using older versions of EBO Workstation as well. 
 
(and also, not related to this but please update to SEAL 1.14.2 since 1.14.1 had some issues that has been fixed in 1.14.2 )

Reply

Link copied. Please paste this link to share this article on your social media post.

Benji
Administrator Benji Administrator
Administrator

Posted: ‎2025-04-15 11:28 PM

0 Likes
0
225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-15 11:28 PM

The attached was previously shared by our colleagues in GEC.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Jagadeesh_01
Lieutenant JG Jagadeesh_01
Lieutenant JG

Posted: ‎2025-04-17 01:43 AM

2 Likes
0
183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-17 01:43 AM

Hi @StefanLundin and @Benji, 

Thanks for the updated version of SEAL tool and procedures to connect. I installed both hotfix (EBO v5.0.3.14002 (CP13) - Patch) and used the latest SEAT tool 1.14.2 to connect to PCT, it is connected now. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of