Purpose
This SEAL Script links Alarm objects in EcoStruxure Building Operation (EBO) to the “right” visualization by analyzing real bindings. It can attachTGML Graphicsdirectly, or—when you choosePanels—it prefers Panels that reference those Graphics. Run it in Preview to validate what would change, then Apply to write to the database.
Run Mode
Paste from Workstation Search
Copy the search result from EBO Workstation and paste it into these inputs. The script extracts valid paths automatically and uses them to:
Attachment Type
Options
The script relies on your Workstation searches to define scope and control attachments. You can paste the entire search result; the script extracts valid paths automatically (paths starting with “/”).
Alarm objects
Candidate attachments (Graphics or Panels)
Menu Objects (optional)
Tip: Start with a narrow scope (one system) to validate outcomes in Preview, then expand.
The script is available in SEAL Script → Standard Scripts.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-15 02:35 PM
This doesn't seem to work for Bacnet Alarms on MPx Controllers. Any ideas?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-15 11:58 PM
I could not replicate the issue. I works just fine with MPx and RPx controllers. But I did find another issue where graphic is added as a content to a panel and not as work area initial path, it would not find the panel.
I attached a test version where that issue I found is fixed.
Remember to set the Base Path to the root of the Automation Server or use the "Servers" folder if setting in multiple automation servers at once.
Are you getting any errors?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-16 08:55 AM
Thanks!
I just tested it again (at least with your updated version) and is does work.
No idea what I did wrong before.
Appreciate the help!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-17 01:52 AM
Awesome! I will update this version to the standard later.