Greetings,
I have the attached network, I cannot seem to recognize why I am not getting all the size cable solution in some of the networks. Can somebody help please, everything seems to be in order but cable size is not showing and not updating the programme.
Kind regards.
Muzi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-31 04:10 AM
Hello Muzi,
As said, the latest release of the international version is made available now.
You can download and install the same from the following location.
https://shop.exchange.se.com/en-US/apps/66328/ecostruxure-power-design-ecodial
Kindly follow the guidance, as provide by previous reply to validate the 'modified project file.'
Best Regards,
Team - Ecodial Expert Support
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-14 03:50 AM
Hello,
Greeting for the day and thanks for reaching us through this forum.
We will come back to you as early as possible with our comments.
Thanks & Regards,
Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-22 12:54 AM . Last Modified: 2022-08-22 01:12 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-22 12:54 AM . Last Modified: 2022-08-22 01:12 AM
Hello Muzi,
As Genghiz already mentioned, during the first round of analysis , it is visible that the application is hanging with an ERROR message saying, 'out of memory exception' on INT 4.9.7.
However, we were successfully able to calculate the project on Dev build of INT 4.9.8. On Calculation, it shows the following error that certain components are not calculated and asks to check the list of alerts. If we check the alerts, we come to know that Ecodial application asks to remove SPD s from the sub level switchboards since there is no sensitive load attached or the cable length is less than 10m.
If we remove these SPD s, except the one in the main switchboard, we can calculate the project successfully without any errors. I have attached the updated file as well.
I will request you to wait for the market release of INT 4.9.8, which should happen by first week of September 2022.
You can open the attached file in the INT 4.9.8 build and it should be calculated completely without any error.
Thanks,
Sayani Sikdar
Ecodial - Expert Support
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-31 04:10 AM
Hello Muzi,
As said, the latest release of the international version is made available now.
You can download and install the same from the following location.
https://shop.exchange.se.com/en-US/apps/66328/ecostruxure-power-design-ecodial
Kindly follow the guidance, as provide by previous reply to validate the 'modified project file.'
Best Regards,
Team - Ecodial Expert Support