Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-29 02:35 PM . Last Modified: 2024-11-22 04:25 AM
Dear All,
I'm trying to configure a control panel used in location with TT earthing system.
For generic load after initial project calculation a RCD is added and since protection device is from Acti9 family, recalculation returns no errors.
For motor load there is a different story.
So after initial calculation a following error is generated:
Which also make sense, but after configuring RCD, error still persist with message:
Does that mean that there is no protective device for motor protection in TT system on offer from SE?
And no, I didn't have "withdrawable" option set to yes.
Does anyone know the solution for this problem? Any advice would be nice.
BR from ZR.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-03 01:30 AM
Hello
Here is our comments on the query;
Cause :
* Along with the motor protection; there is no 'integrated RCD' available.
* As the calculation is already ended up, with not able to find the 'add on RCD'
Suggestion :
The suggestion is to try with the choice of "Separate RCD" to get device selected.
Further :
If the provided suggestion is not working well, then please come back to us with the 'project file (.eac)' for further analysis.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-03 01:30 AM
Hello
Here is our comments on the query;
Cause :
* Along with the motor protection; there is no 'integrated RCD' available.
* As the calculation is already ended up, with not able to find the 'add on RCD'
Suggestion :
The suggestion is to try with the choice of "Separate RCD" to get device selected.
Further :
If the provided suggestion is not working well, then please come back to us with the 'project file (.eac)' for further analysis.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-03 07:06 AM
Dear Genghiz,
After choosing "separate RCD" calculation goes through without error.
Ecodial offers RH10M as separate RCD.
I'm wondering why configuration of motor starter Tesys U even with LUCM, which has integrated RCD function, doesn't go through.
BR
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-09 08:21 PM
Hello
Thanks for the confirmation, that the project file has been successfully completed the calculation.
Further to your inputs;
the possible consideration of motor protection devices with integrated RCD, and the associated selection conditions will be verified with the product development team.
Thanks and Regards,
Ecodial Expert Support.