The above topic has been marked as solved in a thread, However, in the latest version V2 released this May 2024. The above subject is still not resolved.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-18 01:22 AM
Hello EDBAS,
For answering your query,
Diversity factors are considered during modifying of Ks.
Transformer, Cables, Circuit breakers & upstream current (Ib) changing based on diversity factors on each level of busbars/Panels.
For that We have done analysis of 2 perspectives (Enabling operating modes for different diversity factors & Creating 2 projects in same range and different diversity factors).
Case 1: -
Diversity factors are considered during modifying of Ks, upstream current (Ib) changing based on diversity factors on each level of busbars/Panels.
For example, we have created trial projects with 3 operating conditions with
We can see below for all the operating modes Transformer/Cable/Upstream circuit breaker are not same. Its changed with respect to given Diversity factor (Ks).
So, Diversity factors (Ks) are considered for adopting offer solution and range of Transformer/Cable/Upstream circuit breaker/Feeder circuit breakers.
Case 2: -
For this case we have cretaed 2 sysmetrical projects(All the connected loads are same range) but we have changed the Diversity factor Ks as 0.5 for second project.
Network 1 with Diversity factor Ks = 1.
Network 2 with Diversity factor Ks = 0.5.
We can see the below screenshots both projects Transformer/Cables/Upstream circuit breaker are not same. Its changed with respect to given Diversity factor (Ks).
|
Network 1 |
Network 2 |
Transformer/Circuit breaker/Cables details |
Project 2 with 100% loading Ks = 1 |
Project 1 with 50% loading Ks = 0.5 |
MV/LV Transformer |
|
|
TA0 |
3150 kVA |
750 kVA |
Circuit breaker |
|
|
QA 0 |
MasterPact MTZ3 MicroLogic X - MTZ3 50H1 |
MasterPact MTZ1 MicroLogic X - MTZ1 12H1 |
QA 3 |
MasterPact MTZ2 MicroLogic X - MTZ2 32H2V |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 3bis |
MasterPact MTZ2 MicroLogic X - MTZ2 32H2V |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 6 |
MasterPact MTZ1 MicroLogic X - MTZ1 10L1 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 7 |
MasterPact MTZ2 MicroLogic X - MTZ2 20H2V |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 7bis |
MasterPact MTZ2 MicroLogic X - MTZ2 20H1 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 10 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H3 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 11 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H3 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 12 |
MasterPact MTZ1 MicroLogic X - MTZ1 10L1 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
Cables |
|
|
WD 12 |
2x300 Sqmm |
2x300 Sqmm |
WD 11 |
2x300 Sqmm |
2x300 Sqmm |
WD 10 |
2x300 Sqmm |
2x300 Sqmm |
WD 7 |
5x240 Sqmm |
2x300 Sqmm |
WD 6 |
2x300 Sqmm |
2x300 Sqmm |
WD 3 |
7x300 Sqmm |
2x300 Sqmm |
WD 0 |
11x300 Sqmm |
3x185 Sqmm |
Conclusion: -
From the above analysis we came to know that diversity factors are considered during modifying of Ks.
Transformer, Cables, Circuit breakers & upstream current (Ib) changing based on diversity factors on each level of busbars/Panels.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-03 05:43 AM
Hello,
There was an issue in managing the given values (while opening the project file) and this has been fixed during the last release.
Can you please provide some additional information.
Regards,
Team - Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-14 11:06 PM
Hello EDBAS,
Can you please provide some additional information (Screenshots, .eac files & Documents).
Regards,
Team - Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-18 01:22 AM
Hello EDBAS,
For answering your query,
Diversity factors are considered during modifying of Ks.
Transformer, Cables, Circuit breakers & upstream current (Ib) changing based on diversity factors on each level of busbars/Panels.
For that We have done analysis of 2 perspectives (Enabling operating modes for different diversity factors & Creating 2 projects in same range and different diversity factors).
Case 1: -
Diversity factors are considered during modifying of Ks, upstream current (Ib) changing based on diversity factors on each level of busbars/Panels.
For example, we have created trial projects with 3 operating conditions with
We can see below for all the operating modes Transformer/Cable/Upstream circuit breaker are not same. Its changed with respect to given Diversity factor (Ks).
So, Diversity factors (Ks) are considered for adopting offer solution and range of Transformer/Cable/Upstream circuit breaker/Feeder circuit breakers.
Case 2: -
For this case we have cretaed 2 sysmetrical projects(All the connected loads are same range) but we have changed the Diversity factor Ks as 0.5 for second project.
Network 1 with Diversity factor Ks = 1.
Network 2 with Diversity factor Ks = 0.5.
We can see the below screenshots both projects Transformer/Cables/Upstream circuit breaker are not same. Its changed with respect to given Diversity factor (Ks).
|
Network 1 |
Network 2 |
Transformer/Circuit breaker/Cables details |
Project 2 with 100% loading Ks = 1 |
Project 1 with 50% loading Ks = 0.5 |
MV/LV Transformer |
|
|
TA0 |
3150 kVA |
750 kVA |
Circuit breaker |
|
|
QA 0 |
MasterPact MTZ3 MicroLogic X - MTZ3 50H1 |
MasterPact MTZ1 MicroLogic X - MTZ1 12H1 |
QA 3 |
MasterPact MTZ2 MicroLogic X - MTZ2 32H2V |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 3bis |
MasterPact MTZ2 MicroLogic X - MTZ2 32H2V |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 6 |
MasterPact MTZ1 MicroLogic X - MTZ1 10L1 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 7 |
MasterPact MTZ2 MicroLogic X - MTZ2 20H2V |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 7bis |
MasterPact MTZ2 MicroLogic X - MTZ2 20H1 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 10 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H3 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 11 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H3 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
QA 12 |
MasterPact MTZ1 MicroLogic X - MTZ1 10L1 |
MasterPact MTZ1 MicroLogic X - MTZ1 10H1 |
Cables |
|
|
WD 12 |
2x300 Sqmm |
2x300 Sqmm |
WD 11 |
2x300 Sqmm |
2x300 Sqmm |
WD 10 |
2x300 Sqmm |
2x300 Sqmm |
WD 7 |
5x240 Sqmm |
2x300 Sqmm |
WD 6 |
2x300 Sqmm |
2x300 Sqmm |
WD 3 |
7x300 Sqmm |
2x300 Sqmm |
WD 0 |
11x300 Sqmm |
3x185 Sqmm |
Conclusion: -
From the above analysis we came to know that diversity factors are considered during modifying of Ks.
Transformer, Cables, Circuit breakers & upstream current (Ib) changing based on diversity factors on each level of busbars/Panels.