Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84244members
353344posts

Find economical solution for the network

EcoStruxure Power Design Forum

Collaborate with your peers on Electrical Network Design and Calculation Software(Ecodial, Electrical Calculation Tools) - ask questions and get answers from Schneider Electric experts and peers. Share your experience.

HassanShalby
Cadet

Find economical solution for the network

I am working on a Commercial Complex project. I want to know how I can optimize the cost while selecting the equipment for my project in Ecodial?

Tags (1)
1 Reply 1
Genghiz
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
609

Re: Find economical solution for the network

Thanks for your query on this subject of “finding an economical solution”

 

Introduction      :

 

This can be achieved during the ‘electrical network design’ with the help of the ‘selection of protection devices’ by considering the coordination called ‘Cascading.’

This is specific property between the “Schneider Electric” protection devices. This is lab tested and tabulated.

 

Principle             :

 

Cascading between two circuit breakers is achieved by using the tripping of the upstream circuit breaker (A) to help the downstream (load side) circuit breaker (B) to break the current. This allows the selection of downstream devices with lower breaking capacities, and therefore lower cost.

In other words, the upstream circuit breaker helps downstream devices break short circuit currents that are greater than the highest short circuit currents that they can break.

 

This can be explained from the following example(s); 

 

Example 01:

In the following example The network design “without cascading” leads to the selection of “circuit breakers with high breaking capacities.”

 

Cascading without.png  * Icc =   the prospective short circuit current

 

Example 2 : 

Whereas in the following example; 

The network design “with cascading” leads to the selection of “circuit breakers with less breaking capacities at the feeder level.”

This is how the cost of the project is saved by considering the ‘Cascading property between the circuit breakers’.

 

Cascading with.png

 

* Icu = The ultimate short circuit ‘breaking capacity’ of the ‘circuit breaker.’

* Icu reinforced = The enhanced ‘breaking capacity’ received due to the ‘cascading effect’ of the upstream circuit breaker.

 