Ecodial - RCD in conjunction with Circuit Breaker

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Ecodial - RCD in conjunction with Circuit Breaker
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
KrunoslavSever
Ensign KrunoslavSever Ensign
Ensign

Posted: ‎2023-05-15 01:27 AM . Last Modified: ‎2024-11-22 04:25 AM

1 Like
3
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-15 01:27 AM . Last Modified: ‎2024-11-22 04:25 AM

Ecodial - RCD in conjunction with Circuit Breaker

Hellow,

 

I have a designer with a question regarding standalone RCD in a conjunction with a circuit breaker. Ecodial is reporting an error according to picture in attachment. Any ideas regarding that errors? Maybe a suggestion to change equipment? Thank you.

 

Best regards,
K

Attachments
testing.7z
Labels
  • Labels:
  • Power Distribution Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Karthikeyan1
Lieutenant JG Karthikeyan1 Lieutenant JG
Lieutenant JG

Posted: ‎2023-05-16 11:37 PM

0 Likes
0
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-16 11:37 PM

Hello,

 

In Ecodial, we have logic in such a way that any protection device which has a breaking(opening/closing while fault occurs) mechanism, will be displayed as an open/close single-line diagram in the network. 

 

In the case of Standalone RCDs, those are the devices that can break the fault network without the help of Circuit breakers. But, other type of RCDs (Addon, Integrated, and Separated RCD) need the help of a Circuit breaker to make or break the network. 

 

Standalone RCD can do its own decision and do its own operation. So in Ecodial Standalone RCDs are considered switches. Which are available in the place of switches along with RCD. If you enable the switch with Standalone RCD, it will propose the iID and other similar RCCB devices. 

 

If you want to use Standalone RCD along with a Circuit breaker, there are 2 ways to do that in Ecodial.

2 networks.JPG

 

 

 

 

 

 

 

 

 

 

In the above screenshot, you can see that I have added the switch disconnector interconnection after the circuit breaker. 

Option 1: Use CB-Cable-Switch interconnection, then make the cable length 0.01m (Basically consider no cable between circuit breaker and switch). In switch, you need to enable RCD with type as Standalone. If it is a standalone RCD with a switch it will propose iID device as a separate protection device. 

 

Option 2(Preferred option):  Add CB as an interconnection below that add a busbar and then add a switch then connect one more bus bar. In this scenario, both the circuit breaker and switch are connected with the same Bus bar/switchboard. In switch enable RCD with standalone as type. Now it will propose the iID as the standalone RCD as well as switch. 

 

I hope this will clear your doubts. If you need further clarification kindly write it here. 

 

Thanks & Regards,

Ecodial Experts team. 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
AndrejsRo
Crewman AndrejsRo Crewman
Crewman

Posted: ‎2023-05-16 07:16 AM

0 Likes
0
2130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-16 07:16 AM

Hi,

 

I have the same question.

I know that iID are coordinated with iC60.

AndrejsRo_0-1684246568534.png

 

See attached document.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Karthikeyan1
Lieutenant JG Karthikeyan1 Lieutenant JG
Lieutenant JG

Posted: ‎2023-05-16 11:37 PM

0 Likes
0
2118
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-16 11:37 PM

Hello,

 

In Ecodial, we have logic in such a way that any protection device which has a breaking(opening/closing while fault occurs) mechanism, will be displayed as an open/close single-line diagram in the network. 

 

In the case of Standalone RCDs, those are the devices that can break the fault network without the help of Circuit breakers. But, other type of RCDs (Addon, Integrated, and Separated RCD) need the help of a Circuit breaker to make or break the network. 

 

Standalone RCD can do its own decision and do its own operation. So in Ecodial Standalone RCDs are considered switches. Which are available in the place of switches along with RCD. If you enable the switch with Standalone RCD, it will propose the iID and other similar RCCB devices. 

 

If you want to use Standalone RCD along with a Circuit breaker, there are 2 ways to do that in Ecodial.

2 networks.JPG

 

 

 

 

 

 

 

 

 

 

In the above screenshot, you can see that I have added the switch disconnector interconnection after the circuit breaker. 

Option 1: Use CB-Cable-Switch interconnection, then make the cable length 0.01m (Basically consider no cable between circuit breaker and switch). In switch, you need to enable RCD with type as Standalone. If it is a standalone RCD with a switch it will propose iID device as a separate protection device. 

 

Option 2(Preferred option):  Add CB as an interconnection below that add a busbar and then add a switch then connect one more bus bar. In this scenario, both the circuit breaker and switch are connected with the same Bus bar/switchboard. In switch enable RCD with standalone as type. Now it will propose the iID as the standalone RCD as well as switch. 

 

I hope this will clear your doubts. If you need further clarification kindly write it here. 

 

Thanks & Regards,

Ecodial Experts team. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

KrunoslavSever
Ensign KrunoslavSever Ensign
Ensign

Posted: ‎2023-05-17 05:48 AM

0 Likes
0
2100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-17 05:48 AM

Hi, thank you for information. 

 

Best regards,

Kruno

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of