Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

Ecodial Cable thermal constraint solution

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Ecodial Cable thermal constraint solution
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
67
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Power Design – Ecodial

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
ler0ck
ler0ck
Cadet

Posted: ‎2024-04-08 08:17 PM . Last Modified: ‎2024-11-22 04:25 AM

0 Likes
4
1265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-08 08:17 PM . Last Modified: ‎2024-11-22 04:25 AM

Ecodial Cable thermal constraint solution

Hello, I got a problem about cable constraint. I tried modified circuit breaker, increase cable size but no luck.

Do you guy have a solution to solve this warning?

 

ler0ck_0-1712632269099.png

ler0ck_1-1712632336783.png

Labels
  • Labels:
  • Power Distribution Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2024-07-03 06:04 AM

0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-03 06:04 AM

Hello,

This would be a specific network scenario with a small load & less fault currents.

That you will not get a product to sense and protect it from. 

 

If there is no solution of a product is found by the application, this should not stop by throwing an error. 

Suitable improvement request will be communicated to the product management. 

 

Regards, 

Team - Ecodial Expert Support.

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2024-04-15 10:12 PM

0 Likes
0
1236
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-15 10:12 PM

Hello

Thanks for reaching the EcoStruxure Power Design Forum.

Can you please kindly enclose the project file, for the further analysis by the expert team.

What is version of application used for the project file creation.

Thanks

Team – Ecodial Expert Support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2024-07-03 06:04 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-03 06:04 AM

Hello,

This would be a specific network scenario with a small load & less fault currents.

That you will not get a product to sense and protect it from. 

 

If there is no solution of a product is found by the application, this should not stop by throwing an error. 

Suitable improvement request will be communicated to the product management. 

 

Regards, 

Team - Ecodial Expert Support.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

KrunoslavSever
Ensign KrunoslavSever Ensign
Ensign

Posted: ‎2024-08-30 07:20 AM . Last Modified: ‎2024-08-30 07:35 AM

0 Likes
1
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-30 07:20 AM . Last Modified: ‎2024-08-30 07:35 AM

Hello, 

 

I'm having a similiar issue with thermal constraints. @Genghiz Can you please see the ecodial file attached? Please advise solution to clear the problem with thermal constraint. Thank you.

Best regards

Attachments
test 1.eac
Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2024-08-30 09:39 AM

In response to KrunoslavSever
0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-30 09:39 AM

Hello,

The next higher size than the locked one (ie from 16 to 25 mm2 of the cross-sectional area) has avoided this warning. 

 

Team

Expert Support

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore