Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-02-15 10:26 PM . Last Modified: 2024-11-22 04:25 AM
Problem Statement :
While calculating the network with high rated MVLV Transformers, Ecodial ends up with an ERROR message for the cable.
ERROR : No solution found for the cable (WD0). The maximum number of touching circuits (20) is exceeded for the installation method(). reorganize the circuit to decrease the 'number of additional touching circuits.'
Cause :
This is due to the following reasons that;
The Solution :