Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Which software can I configure in EcoStruxure Power & Building Software Companion?

EcoStruxure Power & Building Software Companion

This knowledge base provides you with "how to" articles, support information, and documentation on EcoStruxure Power & Building Software Companion to help you configure and manage your customer software.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • EcoStruxure Power & Building Software Companion
  • Which software can I configure in EcoStruxure Power & Building Software Companion?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AlexandreBoulet
    AlexandreBoulet

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Power & Building Software Companion
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
85 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Which software can I configure in EcoStruxure Power & Building Software Companion?

Administrator AlexandreBoulet Administrator
‎2025-04-08 05:13 AM

At launch, the Software Companion empowers you to configure the following software products: 

  • EcoStruxure Building Operation (from version 7.0) 
  • EcoStruxure Power Monitoring Expert 
  • EcoStruxure Power Operation 

Stay tuned as we continuously expand our portfolio, adding more Schneider Electric software from the EcoStruxure for Buildings suite. 

AlexandreBoulet_0-1744114266572.png

 

As a valued EcoXpert partner, your configuration capabilities are tailored to your EcoXpert badge: 

  • EcoXpert Building Automation: Configure EcoStruxure Building Operation (from version 7.0) 
  • EcoXpert Power Management: Configure EcoStruxure Power Monitoring Expert & EcoStruxure Power Operation 
  • EcoXpert Power Automation: Configure EcoStruxure Power Monitoring Expert & EcoStruxure Power Operation 

Do you hold multiple EcoXpert badges? Unlock an even broader range of software configurations!

 

If you encounter any issues with software selection despite holding the appropriate EcoXpert badge, please reach out to your local Schneider Electric Representative to ensure your account settings are correct.

Labels (1)
Labels:
  • New Features and Annoucements

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of