unplugged virtual sensors

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • unplugged virtual sensors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:58 PM . Last Modified: ‎2024-04-09 02:37 AM

0 Likes
11
1394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:58 PM . Last Modified: ‎2024-04-09 02:37 AM

unplugged virtual sensors

Often the vitual sensors last value is "unplugged" How can I solve this situation? I've alarms associated with these virtual sensors and I nee to read always the right value.

Best regards,

 

Enric Climent

 

(CID:103586332)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:58 PM . Last Modified: ‎2024-04-09 02:37 AM

0 Likes
2
1394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:58 PM . Last Modified: ‎2024-04-09 02:37 AM

Hi Enric,

 

I'm assuming you're seeing this in DCE and not DCO.

What are you using to create the virtual sensors? NetBotz sensors? APC device sensors? 3rd party device sensors?

Are the devices themselves going off-line? 

Do the sensors used to create the virtual sensors go unplugged?

What version of DCE are you using? 

Do they report unplugged for a brief period (a single polling cycle) or extended periods like an hour or more?

How many sensors are doing this?

Are they all created from the same device(s)?

 

Steve

 

 

(CID:103586337)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:58 PM . Last Modified: ‎2024-04-09 02:37 AM

In response to DCIM_Support
0 Likes
0
1394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:58 PM . Last Modified: ‎2024-04-09 02:37 AM

Hi Steven,

Yes, I talking about DCE.

I've created virtual sensors from Netbotz sensors and the phisical sensors doesn't go unplugged, just the virtuals.

DCE version is 7.2.6

The sensors are unplugged for long period of time. I have more than 30 virtual sensor and a half are unplugged. All of them are created from two devices, two Netbotz 570.

Regards,

 

Enric Climent

 

(CID:103586361)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

In response to DCIM_Support
0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

Hi Enric,

 

Maybe there's more to this configuration. Can you please elaborate. When you say they report unplugged for a long period, is that an hour, a day? Maybe they went unplugged and never came back? Has anything on the NetBotz appliance changed? Have the sensors been renamed? Anything? 

 

Is the NetBotz appliance configured / discovered normally or is it set up in post only mode? If many virtual sensors are doing this, it sounds like it's either not communicating every time it is expected or the sensors themselves are potentially not reporting values every time. If you look at the data in DCE (not virtual sensors) and compare the data in the NetBotz appliance itself, do the values seem to match up? Next, compare the DCE data to the virtual data, how do they line up?

 

Steve

 

 

 

(CID:103586362)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

0 Likes
1
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

Hi Enric,


You should not rename the virtual sensors. There is a known issue (k-base FA164229) which, although it should not cause the issue you're seeing, will have issues in different views. I was more concerned with the renaming the sensors being used to create the virtual sensors.

Either way, if the appliance and the data on DCE properly update but the virtual sensor does not, there appears to be an issue with either the virtual sensor itself or it's connection to the NetBotz sensor(s). What I would suggest for a test is to create a new virtual sensor. If you have a sensor that is based on one or more NetBotz sensors, recreate it exactly. Do not change anything about the sensors used or the virtual sensor itself. Does this new virtual sensor have the same issue? If not, does it work OK for a period of time but eventually go into the same state? If it does eventually go into the same state, what, if anything, was done to the NetBotz, DCE, or the virtual sensor in any way? 

 If the device is communicating properly and the target sensors have correct values, I don't know of any way to make the virtual sensors start working again but if we can figure out why it happened in the first place, maybe we can stop it from happening again.


Steve


P.S.

Something else I just thought of, can you try and edit the sensor (not name). Edit the sensor, remove sensor(s) when in the edit window. Next, click add sensors and re-add the same sensor(s).

(CID:103586428)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

In response to DCIM_Support
0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

Hi Steve,

When I say for long time it means always, never change. Only when I rename them, then appears as plugged but after few minutes come back to unplugged state. On Netbotz appliance all seems right and the physical sensors shows values.

It`s very estrange so when I rename the virtual sensor gets value but when I rename back to the original name it come back to unplugged state.

Best regards,

 

Enric

 

(CID:103586610)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

0 Likes
2
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

Hi Enric!

You need to check time settings both for DCE and Netbotz appliances.

I have seen such issue about year ago and the reason was in different time on Netbotz and DCE. The issue was resolved, when I set up NTP syncronization for Netbotz from DCE server.

(CID:103586436)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

In response to DCIM_Support
0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

Good call. I had asked about the data and Enric seemed to indicate that the bot and DCE were OK but not the v-sensor. Although not specifically answered, if there are historical values for the v-sensor, this is indeed the next thing to look at. If there is no historical data, maybe this should be done still but is likely not the issue.

(CID:103586444)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

In response to DCIM_Support
0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

Yes, I've read. I have similar behavior - v-sensor shows values after creation or changes for some (equal to polling interval) and goes to unplugged state after next polling. There were data from physical sensors and everything looks fine, but v-sensors from some Netbotz goes to offline and from some appliances works as expected. So I've investigate this deeper and find out that time on problem botz was different from server time. I assume that it relied to Netbotz's feature to send packet of data instead of momentary sensor values.

(CID:103586463)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

Hello guys,

Thanks for your comments. The problem was due the netbotz regional settings so was different time than the DCE server.

Now the v-sensors are right.

Best regards,

 

Enric Climent

 

(CID:103586521)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2024-04-09 02:37 AM

I had the same problem a couple weeks ago and it was indeed caused by incorrect NTP server settings (thanks, Valentin!). Correcting the settings and rebooting all relevant NetBotz appliances fixed the problem.

 

Tomas

(CID:107448430)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2023-10-31 11:40 PM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:59 PM . Last Modified: ‎2023-10-31 11:40 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore