rPDU proper Power Path

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
4
192

rPDU proper Power Path

This question was originally posted on DCIM Support by Mihalis Koutsakis on 2019-11-27


Hello everybody,

 I have some issues getting the proper power values in a power path that I set up on DCO 8.3.2.

I'm trying to connect a power panel (input : 230(115)/50/Three) with an APC rPDU (model AP8886). The rPDU is connected to the power panel using a 32A L1-L2-L3 phase breaker.

 

 

 

When connected, the rPDU voltage power output appears to be 115/50/Single and is not editable.

 

Using an HP c7000 enclosure G2 that needs input 230/50/Three, I get the message “Server does not support power outlet voltage” on the device properties and a recommendation for the rack “The input voltage setting required by the equipment is not available in current rack”.

 

 

What should I do to have the correct power path and clear the messages?

(CID:152079460)

4 Replies 4
DCIM_Support
Picard
Picard
0 Likes
1
192

Re: rPDU proper Power Path

This answer was originally posted on DCIM Support by Jef Faridi on 2019-12-10


Hi Mihalis,

Assuming that your power settings/configuration on the PDU corresponding to the real setup, then it seems the Power "Input Voltage" settings on your HP c7000 device is incorrect, it is defined (as you've also mentioned 230/50/Three):

But, if you take a look at your rack-pdu Power "Voltage Outputs", it says 115/50/single:

It means that the rack-pdu's outlets can only support 115V/50Hz Single phase!

So you would need to edit the power Input Voltage settings for HP c7000 to support 115/50/Single:

That would resolve the notification problem for you.

Kind regards

(CID:152568861)

DCIM_Support
Picard
Picard
0 Likes
0
192

Re: rPDU proper Power Path

This comment was originally posted on DCIM Support by Jef Faridi on 2019-12-13


Hi Mihalis Koutsakis,

Please notice my answer was based on the assumption that your power settings on the PDU corresponds to real setup. However as Gert has kindly described in detail, most likely you would need to correct the power settings on both PDU (to support 400(230) three phase) and the HP c7000 unit to support 230 single phase (as input voltage).

Kind regards

(CID:152569871)

DCIM_Support
Picard
Picard
0 Likes
0
192

Re: rPDU proper Power Path

This answer was originally posted on DCIM Support by Gert Lehmann on 2019-12-11


I think this all boils down to confusion about how to specify voltage in DCO.

If we look at the specs of the HP7000 it says voltage range 220-240 line-to-neutral and in DCO terms that is a single phase voltage. So in you case the input voltage on the HP7000 should be 230V single.

If we look at the AP8886 it takes 400 3-phase as input (meaning the voltage is phase-to-phase), and since it only has single phase outlets the output is going to be 230V single (meaning phase-to-neutral). So the input/output voltage on the PDU must be 400(230)/Three (which means that the voltage is 400V phase-to-phase and 230V phase-to-neutral)

Now it should work, and the way you achieve 3 phases connected to the HP7000 is by creating 3 individual (single phase) connections; one to each power phase (L1, L2, L3). And since the AP8886 does not have a 3 phase outlet, I would expect that is how it is physically wired up.

The 230(115)V is only used in Trinidad & Tobago, so if that is where your data center is located then you will have to change the HP7000 input voltage to 115 Single - but since that is outside HP specs I am fairly confident that the suggested solution above is the correct one 😉

Regards

Gert

(CID:152569033)

DCIM_Support
Picard
Picard
0 Likes
0
192

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.