"inactivity" threshold?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • "inactivity" threshold?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 01:19 AM . Last Modified: ‎2024-04-02 11:16 PM

0 Likes
4
996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:19 AM . Last Modified: ‎2024-04-02 11:16 PM

"inactivity" threshold?

I am not that experienced in setting thresholds in DCE, something I need to address.  However I have an interesting question posed recently by a combination of a petulant PDU and an inquisitive data centre manager (not to be confused).

A PDU recently decided to stop providing data for power and temperature, this is nothing new, however the PDU did not go offline.  The PDU manually rebooted fine and has been giving us a normal service since.

I would like to know though if a threshold can be written to detect 'flatlining', in other words, the PDU is online but streaming the same EXACT temp and power - for a given period.  Below shows a trace of the culprit.  I should mention the red trace is a different PDU in the same rack.

 

(CID:154404799)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 01:19 AM . Last Modified: ‎2024-04-02 11:16 PM

0 Likes
2
996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:19 AM . Last Modified: ‎2024-04-02 11:16 PM

Dear Nigel Fanning,

Unfortunately, what you want cannot be implemented using thresholds in DCE software.

If I understand you correctly, did all other sensors of this problematic PDU display normal (except power and temperature)? If so, I can only recommend that you look for other ways to solve this problem. Maybe you should just replace the controller for this problem PDU? Or look for another way to make it clear in real time, that this PDU has started working incorrectly and needs to be rebooted automatically.

If you have any more questions, please ask.

With respect.

(CID:154405083)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 01:19 AM . Last Modified: ‎2024-04-02 11:16 PM

In response to DCIM_Support
0 Likes
0
996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:19 AM . Last Modified: ‎2024-04-02 11:16 PM

Thanks but all the sensors (all sockets and environmentals) were the same flatline readings until the reboot.  Unfortunately there are no controllers for these units, only the units themselves.

With so many PDU's to monitor it would be better to automate the monitoring using DCE and not have to do it manually.

(CID:154405136)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 01:19 AM . Last Modified: ‎2024-04-02 11:15 PM

In response to DCIM_Support
0 Likes
0
996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:19 AM . Last Modified: ‎2024-04-02 11:15 PM

Dear Nigel Fanning,

However, I can assure you, that DCE software is not suitable for you to solve this problem.

May I ask you the vendor/model/firmware of your PDU(s)?

Also, is it a problem with just one PDU or many PDUs (or all)?

With respect.

(CID:154405180)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 01:20 AM . Last Modified: ‎2023-10-22 09:35 PM

0 Likes
0
996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:20 AM . Last Modified: ‎2023-10-22 09:35 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of