"The system was unable to save your changes due to an expected error"

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • "The system was unable to save your changes due to an expected error"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:55 PM . Last Modified: ‎2024-04-05 02:29 AM

0 Likes
9
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:55 PM . Last Modified: ‎2024-04-05 02:29 AM

"The system was unable to save your changes due to an expected error"

Hi,

  In DCO after adding device associations for ATS/STS we are recieving the following error message 

The system was unable to save your changes due to an expected error.

The Client will restart and any unsaved client changes will be discarded


At this point the client restarts and all changes are lost. We are currently running DCO 8.2.2.

 

Thanks

 

(CID:129404488)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:55 PM . Last Modified: ‎2024-04-05 02:29 AM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:55 PM . Last Modified: ‎2024-04-05 02:29 AM

Hi Mark,

Is it possible to ask for the following data:

client application.log file (usually located in C:\Users\\.isxo\8.2.2.*\Operations\application.log)

server logs (can be download from webmin interface, Stuxureware DC Operation > Download Log Files > "Download log files")

copy of the latest backup file

screen capture illustrating the location of the ATS device (in DCO) and the device trying to be associated.

I will share my box folder with you shortly, so the data can be shared with me safely (hope it's okay with you), thanks.

Kind regards

(CID:129404525)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:55 PM . Last Modified: ‎2024-04-05 02:29 AM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:55 PM . Last Modified: ‎2024-04-05 02:29 AM

Hi Jef, files added. Thanks!

 

(CID:129405816)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:55 PM . Last Modified: ‎2024-04-05 02:29 AM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:55 PM . Last Modified: ‎2024-04-05 02:29 AM

Hi Mark,

I will check the files and will get back to you as soon as possible, thanks.

Kind regards

(CID:129406736)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2024-04-05 02:29 AM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2024-04-05 02:29 AM

Hi Mark,

We have been studding the log files (client and server logs), that you have kindly provided - issue basically seemed to be caused by configuration/cabling of a rack ATS. To continue the investigations and provide you a solution can I ask for the following:

Copy of the latest backup file (or a backup file that contains the issue)

Screen capture illustrating the location of the problem device (rack ATS) (eg. reproduce the issue, and take a screen capture), thanks.

Kind regards

(CID:129407910)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2024-04-05 02:29 AM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2024-04-05 02:29 AM

Hi Jef,

   Screen shots and backups have been uploaded to box. Many thanks for your assistance.

(CID:129411618)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2024-04-05 02:29 AM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2024-04-05 02:29 AM

Thanks Mark,

I will get back to you as soon as possible,

Kind regards

(CID:129411632)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2024-04-05 02:29 AM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2024-04-05 02:29 AM

Hi Mark,

I have been studding the kindly provided data, running tests, etc. but it is not clear what could be the problem with your ATS model (in U3).

I think the best solution is to remodel it (eg. remove the current model and add a new one), as illustrated I could successfully associate to the similar model (either an existing model from Genomes or take/add a new one from the Genome Library):

Kind regards

(CID:129412622)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2024-04-05 02:29 AM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2024-04-05 02:29 AM

Hi Jef,

    Have tried adding new devices and still get the same error.  It is also happening when I try to associate other ATS's.

 

Thanks

Mark

(CID:129413181)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2023-10-22 09:35 PM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:56 PM . Last Modified: ‎2023-10-22 09:35 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore